Your opinions would be welcomed for a little recent problem.
Fitted a new Crabtree split load CCU in the summer and ever since the customer has complained of nuisance tripping, but when ever I check all seems ok.
Last week I went out again (lucky they are across the road from me) and have built a box to introduce earth leakage from phase or neutral.
RCD will take 10mA but not 20mA, phase to earth (neutral to earth is fine).
The RCD will trip if:-
A light switch, not supplied by the RCD, arcs.
A MCB supplied by the RCD is switched on/off.
The RCD will also not reset with any load applied.
Proved the fault to the RCD by swapping with my own from my CCU and it will take 20mA without tripping.
Wholesaler supplied a replacement but this was worse, in that it would trip when all breakers were made.
RCD is 63A 30mA supplying 4 x 32A, shower and 3 A1 rings.
Has anyone else had similar problems with these RCD's or have I been very unlucky.
P.S. I got the wholesaler to replace the originally supplied RCD as it was not latching every time.
Fitted a new Crabtree split load CCU in the summer and ever since the customer has complained of nuisance tripping, but when ever I check all seems ok.
Last week I went out again (lucky they are across the road from me) and have built a box to introduce earth leakage from phase or neutral.
RCD will take 10mA but not 20mA, phase to earth (neutral to earth is fine).
The RCD will trip if:-
A light switch, not supplied by the RCD, arcs.
A MCB supplied by the RCD is switched on/off.
The RCD will also not reset with any load applied.
Proved the fault to the RCD by swapping with my own from my CCU and it will take 20mA without tripping.
Wholesaler supplied a replacement but this was worse, in that it would trip when all breakers were made.
RCD is 63A 30mA supplying 4 x 32A, shower and 3 A1 rings.
Has anyone else had similar problems with these RCD's or have I been very unlucky.
P.S. I got the wholesaler to replace the originally supplied RCD as it was not latching every time.