Is assessment actually necessary?
As I said before, I don't think it's about the words, and not really about regulations, either - I have been talking about 'BS7671 main bonding' as shgorthand for a direct cable connection back to the MET.I see the point as: -
We all agree the need to bond this bit of pipe and, say, a sink to the DNO earth; what seems to be the problem is what "type" of bond it is, to fit within the definitions in the regulations regulations.
I see the problem with 1 as how you might achieve that in some cases(1) the creation of local equipotential zones (Faraday Cages, if you want) by bonding together all exposed metalwork that could be simultaneously touched, on the one hand and (2) not only doing that, but also connecting the bonded-together metalwork to the MET (and hence the DNO 'earth'), on the other hand.
... in the absence of bonding, I presume you mean? That's obviously bad news if one happens to be touching the wrong two things at the time. Mind you, the same could presumably be true with a TN system (and a failed RCD) if there were a partial L-E fault (i.e. not a dead short) such that the OPD did not operate (quickly or at all); on a bad day, it doesn't need anything like 230V to kill.If your in a pensive mood, think about the failure rate of RCDs, and what happens in a TT if the RCD does fail...
Ah, you've moved the goalposts somewhat, from pipework to what BS7671 calls 'exposed-conductice-parts'. If some of the metalwork which can be touched is part of the electrical system (e.g. the case of a washer), then one obviously has no choice but to have bonding between pipes and the electrical system (CPCs/MET).Take an isolated laundry room, so the washer & dryer are connected to earth via there. say, 13A plugs into the sockets, How would you propose connecting metallic water pipes to those earths?
Indeed, and that should be served by the infamous 'main bonding' from MET to where any conductive services enter the premises, theoretically rendering any other bonding superfluous - until you start talking about your conductive walls and floors. If we forget your walls and floors for a moment (since I don't think that many people consider them, at least directly), that's essentially the argument that would say that no bonding of any internal metallic pipes would be necessary if all services entered the property in plastic - but there appear to be dissenters to that view!The intent of the regs is to turn the whole house into one Faraday cage, not lots of little ones
Ah, you've moved the goalposts somewhat
that in the event of an internal or external fault other metal work could become live at mains voltage and both sets of metal could be touched - then yes it should be done
In that context, I totally agree with you. Previously, this thread seemed to be talking only about bonding pipework together and/or to the MET.....the other metal work I refer to here would include metal bodied appliances, as that is the risk that all this is about (in the main)
There seems to be little point in discussing bonding without realising why and ultimately what is being bonded together, any earthed appliance has to be part of the equation.Previously, this thread seemed to be talking only about bonding pipework
The intent of the regs is to turn the whole house into one Faraday cage, not lots of little ones
I suppose it's all 'belt and braces' really. If main bonding, pipework and CPCs all had zero impedance, then the entire house would be a single equipotential zone and it would be futile/unnecessary to add any additional 'local' bonding within that equipotential zone. Indeed, in practice, I think that's largely true (provided the issue of plastic pipes/fittings is satisfactorily dealt with). As far as a human being susceptible to the effects of electric shock is concerned, it is the local equipotential zone that matters, and I suppose supplementary bonding, when required, serves to make totally sure that there are very low impedance paths between things which can be touched within that local environment, just in case the 'whole house' equipotential zone is not achieving that satisfactorily.Not strictly true if you think of the need to supplementary bond a bathroom. That is creating a smaller equipotential zone with in the larger zone of the house.The intent of the regs is to turn the whole house into one Faraday cage, not lots of little ones
Yes, I've often thought that when I see it mentioned here (usually by westie). I think westie is really using 'Faraday Cage' to simply refer to an equipotential zone.I'm beginning to think the analogy with a Faraday Cage is misleading and rather spurious.
As I see it, with a true Faraday Cage, the concept of an 'extraneous-conductive-part' which could introduce a potential (into the cage) would not really exist - because if such things existed, it wouldn't really be a Faraday Cage.