TT system with earth rod.
There has to be an earth wire from the earth rod to connect the supply transformer star point to the CPC wiring around the house. If that is not there then the RCDs will not operate when there is a live or neutral fault to the CPC. This earth cable can be ? well.... what size is required for the earth in order to carry the 30 or so milliamps of fault current that will trip the RCDs
But the earth rod is also introducing an external potential to the building. So it requires to be bonded to the MET of the system. I understand this wire has to be 10mm as it is a bond to an incoming service and may need to carry a lot of current to ensure the MCB operate on over current.
Perhaps there must be two wires from the earth rod to the MET.
There has to be an earth wire from the earth rod to connect the supply transformer star point to the CPC wiring around the house. If that is not there then the RCDs will not operate when there is a live or neutral fault to the CPC. This earth cable can be ? well.... what size is required for the earth in order to carry the 30 or so milliamps of fault current that will trip the RCDs
But the earth rod is also introducing an external potential to the building. So it requires to be bonded to the MET of the system. I understand this wire has to be 10mm as it is a bond to an incoming service and may need to carry a lot of current to ensure the MCB operate on over current.
Perhaps there must be two wires from the earth rod to the MET.