Not really - that is an interesting, but totally different, question. Were they perhaps concerned that if one had one of eric's infamous "106m rings" (or even just a longish non-eric ring) with the CPC only connected at one end, one could run into Zs problems? By my reckoning 106m of 1mm² has a resistance of about 2.3Ω (at 70°) (which would make it impossible to achieve required disconnection times with a B32 or 30A 3036), whereas with a 106m ring CPC, the maximum resistance from any point to CU is only about 0.58Ω.No more and no less than I can explain why a normal, standard-integrity ring has to have a ring cpc. It it not supposed to carry any significant current, and we all know that with just one path for pc current it is perfectly OK for fault protection, so there is no conceivable electrical reason that I can think of why a string of sockets needs a ring cpc when L&N are a ring. Can you?
I think we've done this one to death. 543.7.2.201 says "... shall be provided with a high integrity protective conductor connection complying with 543.7.1. The following arrangements of the final circuit are acceptable: (i) A ring final circuit with A ring protective conductor...". Is that not saying that "a ring final circuit with A ring protective conductor" is one acceptable way of achgieving the required compliance with 543.7.1?But it does - the regulations say so, so it has one. The integrity of the earthing that that provides is often cited as an advantage of ring finals, BTW, and that is what is considered to be "standard integrity earthing".
I think we've reached the point at which I have to say that I don't really care what the regulations precisely say. There is, as you know, no compulsion to comply with BS7671, and I would be prepared to stand in front of anyone and present my argument that (a) I believe my interpretation to be correct, certainly in terms of the spirit, and probably with the word, of BS7671, but if 'they' took your view that it was non-compliant with BS7671, then (b) present the electrical argument that a ring final with a single CPC ring (and 'separate terminals') was as safe as (and essentially identical to, CPC-wise) a (BS7671-compliant) radial circuit whose CPC had been turned into a ring, and a lot safer than a (apparently BS7671-compliant) radial circuit with a 10mm² (or mechanically-protected 4mm²) single radial CPC. Do you believe that you could successfully contest that electrical argument (if I choose that route rather than BS7671-compliuance)??Maybe it is, and maybe it isn't. But that is what the regulations say - there are different ways to achieve HI earthing. ......... adding a second ring cpc to a circuit which normally has one ring cpc.
Of course it makes a difference.No, it makes no difference whatsoever what the L&N are - please answer the simple question.
I'll answer it when you tell me how many line and neutral conductors there are in this:In the diagram, as drawn, is there one CPC or two CPCs - or some other answer. It's a simple question that you should have no trouble answering.
I'm not refusing to answer it - I'm saying it depends.I can understand you refusing to answer it
Neither.and doing your usual diversionary tactics to obfuscate your refusal (or inability) to answer,
It depends.but it does matter. How many CPCs in the diagram ?
So can it not even be assumed that what you have drawn is compliant with any regulation?I didn't ask anything about what regs it may or may not meet, just how many CPCs in the diagram.
No.No anomaly?... a high-integrity radial needs either two radial cpcs or one ring cpc, and a high-integrity ring needs two rings cpcs. No anomaly.
Not at all. I think the only time I've used "protective conductor" here without "circuit" is in the context of "protective conductor current". But if I am wrong about that then I apologise if it confused you.or, in slightly difference language, there are two protective conductors back to the earth bar. Are you quibbling about some perceived difference between "Protective Conductor" and "Circuit Protective Conductor"??
Indeed.Indeed not, but when they are connected at the socket, those two protective conductors, together, become a ring.
No, it has standard (for a ring final) integrity earthing. If you want to do HIE, you have a number of options, one of which is doubling the number of compliant cpcs. A concept which you accept for radials but brand an anomaly when applied to rings.In terms of the sort of thing we are talking about here, one advantage of ring final circuits is that they have CPC redundancy. This means that (unless you subscribe to the BAS viewpoint) a standard ring final circuit is well on the way to being acceptable as a HI earthing system
It only requires that?(requiring only the 'separate terminal' addition to be fully 'HI', except for BAS)
Well, that would seem to be definitive.(i) A ring final circuit with A ring protective conductor..
You obviously have a different understanding of 'anomoly' than I do.No.No anomaly?... a high-integrity radial needs either two radial cpcs or one ring cpc, and a high-integrity ring needs two rings cpcs. No anomaly.
As I said, I really don't care what the regulations actually say. (even though I believe that they "actually say" the same as what I believe). I would be totally comfortable with forgetting about BS7671-compliance (in relation to this particular issue) and, instead (e.g. to demonstrate compliance with Part P) to present my own electrical argument as to why a ring final circuit with a single protective conductor ring (and 'separate terminals') is satisfactory as high-integrity earthing. ... and, although you have not replied to my question, I doubt that you (or anyone) would be able to successfully contest my (electrical) argument.And it's not "except for me", it's except for what the regulations actually say. You can argue until you are blue in the face that you think they don't mean what they actually say, and that it's OK to certify compliance with BS 7671 by ignoring what they actually say because you think you should do something different to what they actually say, but none of that effort will ever change what they actually say.
Quite - and that's all I've been trying to say, all alongWell, that would seem to be definitive.(i) A ring final circuit with A ring protective conductor..
Not so - one can simply increase the size of the cpc, and still retain a single radial one (for a radial circuit).That's where we disagree. As one can tell by looking at other parts of 543.7, the main concept for achieving HIE is (very reasonably) for there to be more than one path back to the CU earth bar (i.e. 'CPC redundancy'). A radial circuit does not have that, so one has to add something to make it HIE.
Yes it does, because a ring final is required to have a ring cpc. If you want cpc redundancy you have to have two ring cpcs.However, a standard ring final (with one CPC ring) already has two paths, so does not need anything additional to create 'CPC redundancy'
What 543.7.2.201 actually says is that you have to have a high integrity protective conductor connection (not circuit, please note) which complies with 543.7.1.- which is presumably why 543.7.2.201(i) says that a ring final circuit is acceptable as HIE
So has your "well they don't actually mean that" now expanded to include "well they don't actually mean that 543.7.1.203 (iii) is an option for ring finals"?In other words, a standard ring final is (give or take the 'separate terminals' requirement) HIE by design (IMO, one of the very few 'pros' of ring finals!), and therefore needs nothing more to bring it up to the same level of HIE as a radial circuit with 'the necessary additions' (or modifications).
Neither have I, because all of that is an invention of yours.As I wrote yesterday, I think one of the confusions is resulting from the fact that BAS seemingly perceives a difference between "Protective Conductor" and "Circuit Protective Conductor", accepting that the former represents "A path" back to the CU (hence there are two), but regarding the latter ('CPC') as referring to the entire ring of protective conductors (with joints) - in which case there is only one. Where he got those different 'definitions' from, I haven't got a clue.
Blimey - has the penny finally dropped for you about what the regulations actually say?I think this really is getting a bit silly.
Yes.We're not talking about geometry but, in context (since it's what matters to HIE), about multiplicity/redundancy of paths from a point on the ring back to the CU earth bar. Although, geometrically, a ring/circle is only one line, there are two (curved) 'lines' (aka 'paths') between any two points on the ring/circle.
Err, if it does not have only one, how can you verify end-to-end continuity of it?If I understand BAS's reasoning (and use of the terms) correctly, I think he probably believes that a standard circuit has just one "CPC" (no matter what topology/configuration it may have),
No, just more tedious inventions by you.but that it may consist of two or more "protective conductors". Hence all this tedious "one or two" debate!