I think that you and BAS are over-interpreting "the CPC'.
I'm not. I'm doing quite the reverse. It is you who is "over-interpreting" it by going on about it being lots of cmall cpcs so it can't be "a" cpc, or how it has 2 paths so it can be regarded as 2 cpcs.
I'm just looking at it as "the cpc", in the same way that everybody does when they talk about "continuity of the cpc", or "does the lighting circuit have a cpc?"
For a radial sockets circuit, all one has to do is to turn the 'single CPC' into a 'single CPC ring' to satisfy the regs.
Yes - that makes it of "higher integrity" than a standard radial cpc.
Or, with radials, you may use 2 x the number of normal cpcs in order to achieve higher integrity, i.e. 2 radial ones.
Just like with 2 ring finals, you use 2 x the number of normal cpcs in order to achieve higher integrity, i.e. 2 ring ones.
It is both so obviously what the regulations
actually say, and so logical and consistent, that it beggars belief that you flatly refuse to accept it.
OK, it's still not a ring in terms of L and N, but that's not relevant - there is no conceivable electrical reason I can think of that a string of sockets only needs one 'CPC ring' if the L&N don't return to the CU from the last socket but does need two CPC rings if the L&N do return to the CU - can you?
No more and no less than I can explain why a normal, standard-integrity ring has to have a ring cpc. It it not supposed to carry any significant current, and we all know that with just one path for pc current it is perfectly OK for fault protection, so there is no conceivable electrical reason that I can think of why a string of sockets needs a ring cpc when L&N are a ring. Can you?
But it does - the regulations say so, so it has one. The integrity of the earthing that that provides is often cited as an advantage of ring finals, BTW, and that is what is considered to be "standard integrity earthing". Just as "standard integrity earthing" for a radial has one radial cpc. And just as one option for "high integrity earthing" for a radial is twice as many radial cpcs, one option for "high integrity earthing" for a ring is twice as many ring cpcs.
What I don't understand is that BAS (and now maybe you) are arguing about the words of the regs in a manner that results in him (and now maybe you) concluding that there is a requirement to do something which I strongly suspect no-one, or virtually no-one, does, or has ever done.
I can't speak for EFLI, but what I am arguing for is recognition of what the regulations
actually say. And as I have said more than once, I find it unfathomable that so many people either refuse to recognise what they actually say, or they do but then decide that because they don't like, or agree with, or understand what they say they will proceed on the basis that the regulations don't mean what they actually say, and that compliance with them can be achieved by ignoring what they actually say and doing things which they do not actually say.
I suppose it was me that started out, but I was talking about something that seems to be far more of an anomoly - that for a non-sockets circuit, one can satisfy the requirement for HI earthing simply by having a (single) 10mm² CPC - which sounds neither sensible nor safe to me, since mechanical breakage of the CPC (which is about the only useful issue a high-CSA CPC would address) is a very unlikely cause of a hazard arising.
Maybe it is, and maybe it isn't. But that is what the regulations say - there are different ways to achieve HI earthing. One is larger csa, another is twice the normal number of separate cpcs, i.e. adding one which is just like the normal one, i.e. adding a second radial cpc to a circuit which normally has one radial cpc, or adding a second ring cpc to a circuit which normally has one ring cpc.