Softus said:
Okaaayyy, but I got the impression from b-a-s' post that in a non-fault situation the readings will increase, and that it's normal to record the highest reading in the range.
Is that not what happens then?
Its too do with the fact that T&E cable has a reduced CPC
Imagine a ring of 10 units of length total (and we will say the cable has 1 unit of resistance for each unit of length on phase + neutral, and 1.5 on the earth), if we cross connect at the board and put the ohm meter across at a S/O we will be measuring the resistance of 2 ten unit long lengths of cable wired in parralel,
If we are in the middle of the ring, we are seeing 5 units of conductor A in series with 5 units of conductor B all in parralel with the same. If we are a quater way along, we see 7.5 of A, together with 2.5 of B, and thats in parralel with 2.5A + 7.5B.
As long as A and B are the same resiatnce per unit length, it doesn't matter but if they differ, and the readings will increase towards the centre of the ring, just to work it through quickly
A is the phase, B the earth, (2.5x1)+(7.5*1.5) = 2.5+11.25=13.75
(2.5x1.5)+(7.5*1) = 3.75+7.5=11.25
Pop them in parralel and we get 6.18
and for the centre
(5*1)+(5*1.5) = 5 + 7.5 = 13.5
the other half is exactly the same and so you get 6.75 in parallel
If it was phase and neutral instead of phase and earth, it'd always be 10 in parral with 10, giving a reading of 5 whereever you were.
Anyway, hope this helps, might be usful to get a pen and paper and scribble it out (I just did), I hope I haven't made any mistakes with the calulations, and sorry for using silly values just plucked out the air, it makes the calculations easier for proving the physics, oh and I couldn't be arsed to go and look them up