And an Iz of 13.5A with Method 103.It doesn't but it stipulates a minimum csa of 2.5mm² which has an Iz of 27A method C.
What it does stipulate is an Iz of at least 20A. So an Iz of 20A complies,
And an Iz of 13.5A with Method 103.It doesn't but it stipulates a minimum csa of 2.5mm² which has an Iz of 27A method C.
Be that as it may, a BS 1363 socket is not required to remain safe and undamaged if > 20A is flowing in the cable which supplies it.Whatever tests BS1363 may or may not require, I seriously doubt that any significant number of people (if any) have ever done as you suggest for the reason you are mentioning, and I am not aware of any reports of a problem with the 'standard practice'.
Be that as it may, a BS 1363 socket is not required to remain safe and undamaged if > 20A is flowing in the cable which supplies it.Whatever tests BS1363 may or may not require, I seriously doubt that there is any issue relating to a current of 32A (or probably more) passing between two conductors that happen to be joined in the terminal of a BS1363 socket. Those terminals are generally no 'inferior' to those of a 30/32A JB, and if the connection is made securely virtually no heat will be generated at the joint, so there will be virtually no thermal implications for the socket.
Be that as it may, a BS 1363 socket is not required to remain safe and undamaged if > 20A is flowing in the cable which supplies it.To do as you suggest and introduce countless additional ('unnecessary') joints into a radial circuit, as compared with the way in which virtually everyone has always wired such a circuit would seem to me to be undesirable.
No, it is not 'required' to.Be that as it may, a BS 1363 socket is not required to remain safe and undamaged if > 20A is flowing in the cable which supplies it.
Be that as it may, a BS 1363 socket is not required to remain safe and undamaged if > 20A is flowing in the cable which supplies it.
Be that as it may, a BS 1363 socket is not required to remain safe and undamaged if > 20A is flowing in the cable which supplies it.
In which case there are no guarantees pf performance outside that limit which can be relied upon.No, it is not 'required' to.
I am unaware of any guarantees of that which can be relied upon given that there are no requirements for sockets to remain safe and undamaged when 32A is flowing in the supply cable.However, you are surely as aware as I am that, provided the conductors are terminated satisfactorily into the socket's terminals, that 32A flowing in one or both of the cables will have no noticeable effect on the 'remaining safe and undamaged' of the socket.
I'm sure there are no 'guarantees'. However, I am perfectly happy to trust my judgement in this matter - as, I imagine, are the majority of electricians, since I have never heard of one unhappy to wire BS1363 sockets directly into a 32A radial.I am unaware of any guarantees of that which can be relied upon given that there are no requirements for sockets to remain safe and undamaged when 32A is flowing in the supply cable.
In which case there are no guarantees pf performance outside that limit which can be relied upon.
I am unaware of any guarantees of that which can be relied upon given that there are no requirements for sockets to remain safe and undamaged when 32A is flowing in the supply cable.
I have never heard of one unhappy to wire BS1363 sockets directly into a 32A radial.
I would have said so, and, for what it's worth, Appendix 15 of BS7671 shows such a circuit, with a string of BS1363 sockets and a BS1363 FCU on a 4mm² 32A radial.Indeed. Isn't it a standard circuit arrangement?
I'm not at all sure why he has suddenly decided to question the practice!
I've also seen people, when they encounter a regulation which they simply do not like, prepared to employ arguments so ludicrously at odds with clear and unambiguous wording that they border on the delusional.I'm sure there are no 'guarantees'. However, I am perfectly happy to trust my judgement in this matter - as, I imagine, are the majority of electricians, since I have never heard of one unhappy to wire BS1363 sockets directly into a 32A radial.
I would not be happy to use an electrical accessory in a way in which I had no assurance that it would safely carry the currents involved.Do I take it that you would not be happy to connect a "6A rated" ceiling rose, batten holder or switch (if involved in 'looping') to a 10A (or even 16A) lighting circuit?
I am not guessing, or dreaming anything up.Because he is guessing and dreaming up nonsense words to justify his guesswork.
I would be delighted if you were to ignore me.Best to ignore him.
Exactly - and, I would say, "patently ridiculous" for other reasons as well....but why have you just realised this? The logical conclusion is that only one socket may be fitted to a circuit, ring or radial. Patently ridiculous for a ring, for no other reason than a ring would not be required.
No - that is patently illogical....but why have you just realised this?
The logical conclusion is that only one socket may be fitted to a circuit, ring or radial.
I'm attempting to draw the logical conclusions from plain and unambiguously written requirements.Even if an attempt is being made to get some sort Jobsworth Award, he's therefore not even being a particularly good Jobsworth.