Surely you aren't suggesting that a cable with a CCC > 20A will somehow make a current of > 20A appear?
Nope, but nor am I suggesting that it prevents a current >20A flowing. Since a designer has no way of guaranteeing what current will flow in any sockets circuit, all we can really do is talk about circuits that would be BS7671-compliant, and, on that basis, I think that your 'logical conclusions' are not all that logical - or, at least, very 'selective'.
Do I take it that you agree (since this is what BS7671 says) that if (as is very common) one has a ring final wired in Method C 2.5mm² cable, that it will be fully compliant if the designer has satisfied himself/herself that no part of the cable is "likely to carry more than 27A for long periods"?
I also assume that, since you keep saying it, that you agree that BS1363 offers no guarantee that a socket to that Standard will "remain safe and undamaged" if the current in the attached cables exceeds 20A. Is that correct?
You have also stated, more than once, that you would not be happy to use an electrical accessory in the absence of such a guarantee, and that you would advise others likewise. Is that correct?
If the answer to all three of those questions is 'yes', then the 'logical conclusion' would seem to be that you would not be happy to connect BS1363 sockets directly to a BS7671-compliant Method C 2.5mm² ring final, and would advise others accordingly - unless, that is, unless you (or they) have some crystal ball that would enable you (or they) to guarantee that none of the cable would ever carry more than 20A.
Do I also take it that you believe that the diagrams of both ring and radial sockets circuits in Appendix 15 of BS7671 are 'incorrect' and unsafe?
Kind Regards, John