Is it overcurrent protection on the N?
Which is not normally provided anyway.
If there is over current on the Neutral that is coming from a Live to Neutral path ( fault or overload ) then the over current on the Live will trip the MCB mechanism.
If there is over current on the Neutral that is NOT from a Live to Neutral path then the difference in Live and Neutral currents will trip the RCD mechanism.
That assumes that the RCD sensor will react to a very high difference in Live and Neutral current. A very large difference may saturate the sensor in the RCD. The very high difference would normally be Live current greater than Neutral current and hence the MCB would operate