If you mean a PP setting?? of 4.0M then this shouldn't cause problems, or was/is it set to CP 4.0M, see below.Many thanks again for your very useful suggestions. Presently not at home but will be back around mid day. Pump was on 4.0 and PV setting. It shows the power setting but I don't think flow. Was also set on dynamic setting but turned this off.
The pump (as you probably know) apart from C1,C2&C3 modes, will flash the set head pressure for a few seconds and then display the power, W,
I have mine set to PP (proportional pressure) at 4.6M which gives a actual head of ~ 3.6M with all the (10 rad) TRVs open and ~ 2.7M when they throttle down, the second photo shows a CP (constant pressure) setting of 4.0M., For info, C1=constant curve 2M, C2=constant curve ~ 3.8M & C3=constant curve 6M.
You could try a CP setting starting at say 2.5M, if no air problems then but if rads a bit slow to heat up, you can gradually increase the SP incrementally in 0.1M steps to get the optimum setting.
I have a 50 year old open vented system with some rads over 40 years old, never gave/gives any sort of air ingress problems because of the way it was installed over 50 years ago with a true combined vent& cold feed, I have seen VCP systems converted to my type which cured the problem despite havin a perfectly clean VCP systemAnother bit of information which could negate potential blockage. Have tried the magnet test on all pipes in that area and no pull detected. I did this test 10 years ago and had several areas to replace