Read it again. It says "In each installation main protective bonding conductors complying with Chapter 54 shall connect to the main earthing terminal extraneous-conductive-parts including the following:"
(iv) Central heating
Yes,
IF the central heating system is an extraneous-conductive-part. If it isn't, then it does not need bonding.
Do you actually understand what an extraneous-conductive-part is, and what causes it to become an extraneous-conductive-part?
Are you saying radiators, pipes and boilers can never be extraneous-conductive parts?
Not never, but very very rarely.
The central heating is virtually bound to be connected to the gas and water.
Nevertheless it is specifically mentioned in the regulations as needing MAIN protective bonding?
I'll say it again.
Only if it's an extraneous-conductive-part, which if it is like 99% of heating installations in this country then it will not be. Being connected to the gas and water or not has no bearing on whether it is an extraneous-conductive-part, and I don't believe you actually understand what makes some metal work an extraneous-conductive-part, and others not.
well i don't know if this is relevant to it ..
No it isn't really.
a few years ago my electricity was tripping the rcd on the odd occasion ...i did not put two and two together....and work out that it was the immersion heater .until after about the 3rd or 4th trip ..when it didn't want to reset ..
until i turned off the immersion mcb.
a day or two later i investigated .took the immersion heater out ..and it had rotted.......the copper covering the elements was gone in places ..and the inner core was exposed .
Nothing would have happened. Your immersion heater is an exposed-conductive-part and is earthed so that in the event of a fault, the circuit is automatically disconnected, exactly as your circuit did.
Earthing is completely different to bonding, as as you can see from your own example it provides a different function to bonding all together.
i had non of this earth bonding then, except the water main and the main electric riser . ..but ..it lead me to think of ..what if i was having a bath when this happened ..
Bonding would have made no difference at all. Bonding is not there to provide automatic disconnection in the event of a fault.
Merely pointing out what is in the regulations.
I know exactly what is written in the regulations, but it appears you don't actually understand what it means.
Then statements like this are written -
411.3.1.2 does not apply to radiators, pipes and a boiler in a normal house, because none of those items will be extraneous conductive parts.
I agree 411.3.1.2 does not apply but do you agree with the rest of it.
Agree with the rest of what? Regulation 411.3.1.2 is entirely correct. It is just that it does not apply to central heating systems which do not contain any extraneous-conductive-parts, i.e. virtually all domestic heating systems.