Earth rod installation

Joined
6 May 2013
Messages
83
Reaction score
20
Country
United Kingdom
Hello all,

I just had my garden room certificated by an electrician. He said the earth reading is high but it passed but he advised to install an earth rod, I did ask before the installation if an earth rod would be needed but was told the house earth is enough I should have insisted on an extra earth rod but you try and leave it to the professionals.

I believe I have a TT System, got live and neutral coming in and earth going out to an earth rod on the house.

The consumer unit is on an internal wall and running a new earth cable is somewhat not possible. However I already have a 10mm earth for water pipe bonding on an outside wall, that is connected straight to the consumer unit. So can I just run another 10mm from that pipe to an earth rod or do I have to run a new earth cable to the consumer unit.

Thank you.
 
Sponsored Links
He said the earth reading is high but it passed but he advised to install an earth rod,
What was the reading?
What is the house reading.

I did ask before the installation if an earth rod would be needed but was told the house earth is enough I should have insisted on an extra earth rod but you try and leave it to the professionals.
You said it 'passed'.

I believe I have a TT System, got live and neutral coming in and earth going out to an earth rod on the house.
TT is a system that uses an earth rod.

The consumer unit is on an internal wall and running a new earth cable is somewhat not possible. However I already have a 10mm earth for water pipe bonding on an outside wall, that is connected straight to the consumer unit. So can I just run another 10mm from that pipe to an earth rod or do I have to run a new earth cable to the consumer unit.
You don't need to.

IF necessary just earth the garden room with its own rod.

Is the garden room a distance from the house or just an extension?
 
Hi, I don't know, all he said the reading is high but it is still a pass, I guess over time that this can worsen so he suggested a earth rod for the garden room.

Sorry I was talking about the garden room regarding the internal wall. I can either run from the pipe bonding (the garden room has a bathroom) to the rod without to much trouble but if I need to run from the CU I will need to have a cable channel along the wall which I would like to avoid.

Edit: Garden room is 40m away from the house, the SWA (3 core) is 25mm and about 60m long.
 
Sponsored Links
BS 7671:2008 Table 41.5 said:
NOTE 2:* The resistance of the installation earth electrode should be as low as practicable. A value exceeding 200 ohms may not be stable. Refer to Regulation 542.2.2.

200Ω is quite high, normally more like 60Ω with a 30 mA RCD it can go to 1667Ω, but it will show on the paperwork what it is, so what does it say?
 