Zs must not be measured with the bonding disconnected.
Ze must be measured in isolation, i.e. with the bonding and the exposed conductive parts disconnected to remove any parallel paths. The installation must be isolated whilst this test is carried out and the means of earthing reconnected before the system is energized.
What is the Ze (or Ra) of the electrode?
Ze must be measured in isolation, i.e. with the bonding and the exposed conductive parts disconnected to remove any parallel paths. The installation must be isolated whilst this test is carried out and the means of earthing reconnected before the system is energized.
What is the Ze (or Ra) of the electrode?