Right then, bloke rang me say he has had a EICR done with the following codings.
The whole place was rewired in 2004
1 No RCD on bathroom lighting C2 N/A
2 No RCD on kitchen lighting. C2 N/A
3 No danger notices on consumer unit C3 N/A
The board results are
1 Lighting A 100 7 1.5 1.0 0.4 60898 B 6 6 7.67 0.41 N/A > 200 > 200 > 200  0.65
2 Lighting A 100 6 1.5 1.0 0.4 60898 B 6 6 7.67 0.64 N/A > 200 > 200 > 200  0.87
3 Spare
4 Spare
5 Spare
6 Spare
7 Outside Supply A 100 1 4 2.5 0.4 60898 B 32 6 1.44 0.14 N/A > 200 > 200 > 200  0.32
8 Sockets Kitchen A 100 7 2.5 1.5 0.4 60898 B 32 6 1.44 0.41 0.41 0.52 0.30 N/A > 200 > 200 > 200  0.43
9 Sockets Flat A 100 8 2.5 1.5 0.4 60898 B 32 6 1.44 0.44 0.45 0.56 0.33 N/A > 200 > 200 > 200  0.47
D.B. 1 Bedroom 25 kA N/A
Surely in 2004 the outside supply and the sockets should have been on RCD but NOT the lighting?
The inspector included a quote for a new board, I would have thought RCBOs would have been easier?
I wonder why he has singled out the bathroom and kitchen for speciaql attention.
The whole place was rewired in 2004
1 No RCD on bathroom lighting C2 N/A
2 No RCD on kitchen lighting. C2 N/A
3 No danger notices on consumer unit C3 N/A
The board results are
1 Lighting A 100 7 1.5 1.0 0.4 60898 B 6 6 7.67 0.41 N/A > 200 > 200 > 200  0.65
2 Lighting A 100 6 1.5 1.0 0.4 60898 B 6 6 7.67 0.64 N/A > 200 > 200 > 200  0.87
3 Spare
4 Spare
5 Spare
6 Spare
7 Outside Supply A 100 1 4 2.5 0.4 60898 B 32 6 1.44 0.14 N/A > 200 > 200 > 200  0.32
8 Sockets Kitchen A 100 7 2.5 1.5 0.4 60898 B 32 6 1.44 0.41 0.41 0.52 0.30 N/A > 200 > 200 > 200  0.43
9 Sockets Flat A 100 8 2.5 1.5 0.4 60898 B 32 6 1.44 0.44 0.45 0.56 0.33 N/A > 200 > 200 > 200  0.47
D.B. 1 Bedroom 25 kA N/A
Surely in 2004 the outside supply and the sockets should have been on RCD but NOT the lighting?
The inspector included a quote for a new board, I would have thought RCBOs would have been easier?
I wonder why he has singled out the bathroom and kitchen for speciaql attention.