Electric shower tripping MCB

Joined
13 May 2014
Messages
33
Reaction score
1
Location
Merseyside
Country
United Kingdom
Newly installed Triton T80 8.5kW shower. The shower is tripping the MCB after about 5mins of use since it was installed. It’s on an 40A MCB which feels warm to the touch after it trips. Appears to be 6mm cable, the consumer unit is less than 18m away. No sign of water leaks, completely dry inside the case. Trying to get the guy who installed it to come back and fix, would be good to know possible causes/remedies before being fobbed off.
 
Last edited:
Sponsored Links

Attachments

  • 5BE7B70E-E48F-47AC-9AE8-A80B9B633983.jpeg
    5BE7B70E-E48F-47AC-9AE8-A80B9B633983.jpeg
    263 KB · Views: 146
  • C8A60AC7-2481-4D62-B955-CD3399E58F25.jpeg
    C8A60AC7-2481-4D62-B955-CD3399E58F25.jpeg
    201 KB · Views: 135
That device is an MCB ,not an RCD.
Are you sure the shower is 8.5kw ? The 40amp breaker isn't going to be tripped on overload by an 8.5kw shower alone ,it would trip if there is a short circuit though.
The MCB's on that board don't appear to be fitted very well ,and are askew. Why someone would fit 2 from another manufacturer is anyone's guess.
 
Last edited:
Sponsored Links
That device is an MCB ,not an RCD.
Are you sure the shower is 8.5kw ? The 40amp breaker isn't going to be tripped on overload by an 8.5kw shower alone ,it would trip if there is a short circuit though.

Ok thanks will try to amend my OP. With a short circuit would it be likely to run for 5 mins before tripping?
 
That device is an MCB ,not an RCD.
Are you sure the shower is 8.5kw ? The 40amp breaker isn't going to be tripped on overload by an 8.5kw shower alone ,it would trip if there is a short circuit though.
The MCB's on that board don't appear to be fitted very well ,and are askew. Why someone would fit 2 from another manufacturer is anyone's guess.

Check the kW rating on the plate on the underside of the shower.

Can confirm it’s 8.5kw
 