Morpheus83uk, you seem to be getting confused between a RCD and a MCB. They are different devices and NOT the same.
MCB's will have a letter being either B,C,D followed by a number being either 3,6,10,16,20,32,40, 45,50, or 63. The number refers to how many amps the circuit is rated for, think of it like a 3 vs 13 amp fuse in the plug - Higher number for higher powered circuits. (i.e. B16 refers to a type B MCB rated for 16 amps.)
MCB's will normally only take 1 space up in the consumer unit.
RCD's on the other hand are devices that protect against residual current leaking through earth - They are the same type of device you might plug into a electric lawn mower for example to reduce the chance of a fatal electric shock should a electrical fault occur. (i.e. you mow over the wire.)
RCD's will normally take 2 spaces up in the consumer unit.
By your description, it sounds like your boiler and light are both on the same 16 amp type B MCB. If this is the case, the light needs to be on a switched FCU with a 3 or 5 amp fuse in, and the boiler on a swithed FCU with a 3 amp fuse in.
Just to clarify, you need two switched fused spur units (one for the light and one for the boiler) what operate independently of one and other.[/quote]