Well, so you can all sleep tonight without worrying about how many mA it is ...
here ... is .... a .....
photo!
Poo. You guys win!
Well, so you can all sleep tonight without worrying about how many mA it is ...
here ... is .... a .....
photo!
They are both reasonable. It will easily take that length of time (plus more to write up the Report).Well, the first guys that looked said £200 for the test, and today another said he'd test for £160.
Does that sound reasonable? He said it would be 3-4 hours work. Seems a long time for my little bungalow! But cheaper than the first.
How can you condemn something which has not failed anything?The only reason I condemn most installations following periodic inspection and testing is because most are complete and utter ****e.
Can you?Can I rewire the house, if I choose to?
I did wonder if that might be the case - but, as you have seen, there are some people who always 'see/assume the worst' in everything they hear or read!...But that was the Royal "I"!
There's nothing 'strange' about TT (I have it, for a start!). Even though it is gradually becoming less common, the is still an awful lot of it about.What I should have asked is, given that I have this strange (maybe only to me!) TT type of electric, can the house still be rewired, or would I need something altered in the incoming power before that can be done.
Where the supply is overhead the DNO may refuse to offer an "earth" and will insist that the install is TT.In fact, it's not a foregone conclusion that your DNO would be able/willing to provide an earth
One might have thought so, and it might be true of literally overhead (i.e. 'suspended') sinces, but it's certainly not true as a generalisation for 'outdoor supply singles' with my DNO.Where the supply is overhead the DNO may refuse to offer an "earth" and will insist that the install is TT. .... If the supply is two separate wires ( and not a single cable with both Live and Neutral in a single outer sheath ) then TT is the only safe option.
All true, but particularly in the case of a break in a CNE conductor supplying a single property, what you describe would presumably not in itself be directly hazardous if all the necessary main bonding was in place (i.e. if the interior of the property were an equipotential zone)....The risk in a two wire drop of the Neutral wire snapping while the Live remain intact is too high to be acceptable. In PME systems the Neutral supply wire also provides the "Earth" for the installation, if it breaks with the Live still intact then the "Earth" in the house becomes Live.
All true, but particularly in the case of a break in a CNE conductor supplying a single property, what you describe would presumably not in itself be directly hazardous if all the necessary main bonding was in place (i.e. if the interior of the property were an equipotential zone).
is considered "safe" from incidemt that would result in one conductor snapping.3P+N 'ABC cable'
We know that (particularly given the number of times it has been mentioned here!!), but that risk is no different with a lost overhead 'single' CNE than it would be with an underground one within a multi-core cable (and, as we know, once in a blue moon the latter do develop CNE-only faults) - so that point is irrelevant to this discussion.External water tap would need to have a one metre long non-conductive section in the pipe supplying it otherwise the tap would be 230 volts above ground potential. Similar concerns for gas pipes in the outdoor meter box.
Presumably it is, but I would not have thought that the same would be true of the lengthy and iffy run of ordinary singles along my neighbour's wall, would you?[ABC cable] ... is considered "safe" from incidemt that would result in one conductor snapping.
Far less likely to snap due to being stretched tightly as an overhead between two anchoring points.the same would be true of the lengthy and iffy run
Yes, I'm not disagreeing with that, but the consequences of it breaking (e.g. in relation to the infamous 'outside tap'), if it does, would be exactly the same as if it were an underground cable. Since you raised the 'outside tap' (or 'gas meter box') issue, I thought you were implying that it was in some way specific to overhead cables.Far less likely to snap due to being stretched tightly as an overhead between two anchoring points.
As I said, I'm not disagreeing with that.The risk of a lost Neutral and hence "Earths" of a PME rising to 230 volts above ground is far greater in an open wire overhead supply than is is in any other distribution system.
Yes, deriving an "Earth" from a Neutral does concern me. Reason for that is experience of Neutral bounces and high currents flowing to the ground rod from the PME "earth".this is a matter of concern for you even when the supply in not overhead.