Have you just switched off the switch on the sockets downstairs or have you physically removed every plug from every socket?

If not done yet unplug every appliance from every socket downstairs and see if the circuit can be switched on with nothing plugged in.
Thank you for your reply. I have walked round again and unplugged one more. So that is every plug pulled out downstairs but it is still tripping when I flick the switch up.

I keep thinking it’s connected to the smart meter because it seems such a big coincidence. Could a faulty installation cause issues?
 
Sponsored Links
I have found something that could be connected.
We have had lots of rain in the area and I have a conservatory. So could be water/dampness causing issues.

The switch is inside the main house though and not near water.

The light switches to the light and fan isn’t working. I’ve not used the conservatory for a while so don’t know if this is recent though.

I am a but confused because I think it should trip lights downstairs switch rather than sockets downstairs?
 
Whatever you were doing with the Smart meter display at the time is a complete red herring as it's a read-only display device, it doesn't make the meter itself "do" anything.

It's far far more likely to be something on the circuit, are there any hardwired appliances downstairs that may not have an obvious plug to remove, they might have a isolation switch?
 
I have found something that could be connected.
We have had lots of rain in the area and I have a conservatory. So could be water/dampness causing issues.

The switch is inside the main house though and not near water.

The light switches to the light and fan isn’t working. I’ve not used the conservatory for a while so don’t know if this is recent though.

I am a but confused because I think it should trip lights downstairs switch rather than sockets downstairs?
Is there an FCU in the room ( perhaps near the door ) adjacent to the conservatory that might supply the lights and fan off the downstairs ring.
 
Sponsored Links
The RCD measures current in and current out, and if within around 27 mA of each other it assumes nothing has gone to earth. The problem is either line or neutral to earth and it can trip, and the neutral is often not switched.

So switching off often does not help, only unplugging, even turning of a overload (switches in the consumer unit) may not remove the fault.

So we look for a likely cause. The more power used, the greater the difference between neutral and earth, so even if the fault is on the lights, the load on sockets may make it trip, so now you have tried to unplug all you can, next is look at likely items which may have got water in, outside lights, outside sockets. Sockets under the sink supplying the waste disposal unit, clearly shower isolator off, etc.

I had it when my balcony leaked, water went into socket under it. And it actually damaged socket only option was a new one.

When the power can't be switched on we use an insulation tester, these use 250, 500, or 1000 volt to find the fault, the 9 volt used in a multi-meter is often not good enough. The meters are not cheap, so really electrician needs to be called. You have not said where you live, if you lived close I would pop around.

With a switched FCU make sure switched off, just pulling fuse not good enough.

The regulations actually say "Every installation shall be divided into circuits, as necessary, to:
(i) avoid hazards and minimize inconvenience in the event of a fault" but continue to say "
(iv) reduce the possibility of unwanted tripping of RCDs due to excessive protective conductor currents produced by equipment in normal operation (17th ed)
(iv) reduce the possibility of unwanted tripping of RCDs due to excessive protective conductor (PE) currents not due to a fault (18th ed)"

It does seem to on one hand say faults should be considered then 3 lines down say they need not be considered, PE stands for protective earth, however it does seem to say these PE currents should be measured, and back in 2008 before I retired we did not really measure the back ground leakage, we are now told should be less than 30% of the RCD rating (9 mA with a 30 mA RCD) but for years we fitted duel RCD consumer units without really paying much attention to back-ground leakage.

There are other things as well, pre the RCD age we would split rings left and right of a house, so if there was a fault it would not require an extension lead up/down stairs, and also the load was more even between the rings, and it used less cable, so better loop impedance and cheaper. But this "minimize inconvenience in the event of a fault" was read as arranging circuits so one RCD tripping would not cause loss of both lights and sockets in any one room, it was hard to split lights side to side, so sockets were split up/down so upper sockets would be on same RCD as lower lights.

With the advent of RCBO's there is no need for upper/lower split with sockets, but now it has become standard practice, we have the "we have always done it this way" culture, who do not consider why.

As to changing things to stop a repeat in the future, I looked for the WCED make and RCBO's are £9.99 each, I had not heard of
1735736770199.png
before, so likely it will require mail order, is £60 worth it not to loose all?
 
Last edited:
The RCD measures current in and current out, and if within around 27 mA of each other it assumes nothing has gone to earth. The problem is either line or neutral to earth and it can trip, and the neutral is often not switched.

So switching off often does not help, only unplugging, even turning of a overload (switches in the consumer unit) may not remove the fault.

So we look for a likely cause. The more power used, the greater the difference between neutral and earth, so even if the fault is on the lights, the load on sockets may make it trip, so now you have tried to unplug all you can, next is look at likely items which may have got water in, outside lights, outside sockets. Sockets under the sink supplying the waste disposal unit, clearly shower isolator off, etc.

I had it when my balcony leaked, water went into socket under it. And it actually damaged socket only option was a new one.

When the power can't be switched on we use an insulation tester, these use 250, 500, or 1000 volt to find the fault, the 9 volt used in a multi-meter is often not good enough. The meters are not cheap, so really electrician needs to be called. You have not said where you live, if you lived close I would pop around.

With a switched FCU make sure switched off, just pulling fuse not good enough.
This is really helpful, thank you. I’m going to have a look for some numbers for an electrician. We have 2 outside lights above the front door. An outside socket and security light at the back that hasn’t worked in ages. I think I have tried everything I can and now need an expert. I’m based in Manchester.
 
Yes, will call an electrician. Thank you for your help so far. I don’t really understand it and not sure how to check how many socket points are not working because all downstair socket switch has tripped.

Never trust labelling of fuseboards / consumer units
 
If there is, then turn that off and try reset again.


Is there an FCU in the room ( perhaps near the door ) adjacent to the conservatory that might supply the lights and fan off the downstairs ring.

I think you should really look for a switch (and rectangular FUSE) by your conservatory. It will be low level by your sockets. If you find it, switch it off, and then try a reset mcb. That will likly prevent any water in your light and fan causing the RCD to trip.
 
We have a few FCUs. All look slightly different.

Conservatory (no switch).
Hob (no switch)
Oven (has a switch)
Boiler (no switch)
 
try pulling the fuse out of the conservatory one. and then reset

And if the boiler isn't working, remove that fuse if no luck.

I assume the oven and hob work ok in the extension?
 
We have 2 outside lights above the front door. An outside socket and security light at the back that hasn’t worked in ages.
I would open them all and look for water. Look at most outside lights and the PIR is at the bottom 1735739828384.png just waiting for any water to run down into the PIR, last house I drilled a small 1/16" hole in bottom to let water out, but to drill without hitting any components in the PIR is hard, I removed it to drill hole, this house don't use PIR's.
 
I would open them all and look for water. Look at most outside lights and the PIR is at the bottom View attachment 367627 just waiting for any water to run down into the PIR, last house I drilled a small 1/16" hole in bottom to let water out, but to drill without hitting any components in the PIR is hard, I removed it to drill hole, this house don't use PIR's.
Hmm water surface tension would prevent any water draining through a 1/16" hole.
 