Clearly not - but what would you suggest as a practical alternative? The cable needs protection as do the final circuits. You could omit the 32A MCB in the shed (but run the lighting off a 6A local MCB or FCU), hence relying only on the 40A MCB in the main CU - but then you would then not be able to use a 2.5mm² for a ring final or 4mm² for a radial final in the shed.Does that set-up achieve discrimination?
ok all taken on board, i think i will stick with the 16mm swa and 40 amp mcb at the house CU though incase i ever want too add on too the shed supply CU. i.e pond pump etc.
thanks for the advice
Indeed it would, but the "etc." might possibly take a lot moreA pond pump will use less than your lights.ok all taken on board, i think i will stick with the 16mm swa and 40 amp mcb at the house CU though incase i ever want too add on too the shed supply CU. i.e pond pump etc.
Seriously, though, maybe I'm too allergic to digging (or approaching an age when I couldn't do digging!) - but, with a task like this, I would usually always 'go up one size' relative to size of SWA I currently needed, or could envisage needing - simply because there are often unexpected surprises in the future (and, as I said, it's only about a 23% increase in cable price)!
The digging I'd feel obliged to do in order, as a matter of principle, to avoid paying £215.05 + VAT (aka about £2582) to hire a toy for a day!
Clearly not - but what would you suggest as a practical alternative? The cable needs protection as do the final circuits. You could omit the 32A MCB in the shed (but run the lighting off a 6A local MCB or FCU), hence relying only on the 40A MCB in the main CU - but then you would then not be able to use a 2.5mm² for a ring final or 4mm² for a radial final in the shed.Does that set-up achieve discrimination?
Personally, I'd prefer to live with the lack of discrimination than have to wire the shed's sockets in 'shower cable'
Kind REgards, John.
It might be a (very occasional) PITA but, as I was implying, the only realistic alternative I can think of would be more-or-less as big a PITA - namely to have the house MCB as the one and only protection (with either a 32A MCB, or a 40A one with oversized socket cabling in the shed), which therefore would obviously trip (in the house) in the event of a fault in the shed.Just pointing out a non-compliance that could be a PITA if the house MCB trips in place of the local CPD's....Personally, I'd prefer to live with the lack of discrimination than have to wire the shed's sockets in 'shower cable'
Indeed so - that was what I was implying.So it seems this reg. is being watered down over time. To my mind, Where necessary to prevent danger makes the reg. all but redundant. Failing to achieve disc, I mean selectivity does not really give rise to danger, only inconvenience.
Exactly. In fact, when it's a matter of fuse vs. MCB, in the presence of a very high fault current, I suspect that the MCB is very likely to operate first, almost regardless (within reason) of the relative In's of the two devices.Agreed. Think about your average 13A 1362 fuse protecting an appliance connected to a 32A MCB. I have come across 100's of instances over the years where the breaker has popped before the 1362.
And the OP might possily not have a clue what he's doing.the "etc." might possibly take a lot more :-
Whilst I agree with the spirit of what you're saying, that statement is surely way OTT? If the finding of "one single thing" that one doesn't understand or which makes one think "I never knew that" indicated that one should turn to some other (presumably omniscient) person to undertake electrical work, then I would suggest that there would not be any 'competent' electricians to turn to! .... Hands up any electricians who have never said "I never knew that" and who have never found 'one single thing' that they don't understand!If, when you read through this topic, including all of the information linked to, you find one single thing which you don't understand, or even makes you think "I never knew that" then please take that as a sign that you should be using an electrician for this work rather than DIYing it.