Please sir, please sir. My hand's up. I didn't know that the regs on discrimination between protective devices had been watered down.
I'm sure that if they were being honest and forthcoming, the hands of all the electricians here would be up (in relation to something they didn't know/understand, not necessarily discrimination) - so you're in very good company!
Please Indeed even if "selectivity" is necessary to prevent danger you only need to consider selectivity under the rule.
Quite - that's part of the 'watering down' which has apparently happened - and, as I said last night, for once I think the current regs are probably being sensible.
It's fortunate you don't need to do anything about it since such situation regularly occurs in garage/workshop supplies. Often a 32A breaker in the house feeds a 32A breaker protecting a ring circuit in the workshop. Tripping of the house breaker will shut down the lights where machines may still create a cutting hazard in the dark whilst they run down after loss of power.
That's certainly a potential danger, but it's
not anything to do with discrimination/selectivity (per 536 of the regs) - which is about discrimination
between protective devices (and your scenario relates to the operation of only one). However, although the discrimination regs have been watered down, others have been tightened up. 314.1 now says:
"Every installation shall be devided into circuits, as necessary, to:
(i) avoid hazards and minimize inconvenience in the event of a fault
Note that this says 'shall', rather than 'shall consider'. The potential danger you mention will exist whenever a shed/garage where power tools etc. may be used has an electricity supply which shares any protective devices (MCBs and/or RCDs) with any circuits in the house - which is quite common (mainly in relation to RCDs), but seemingly probably non-complaint with 314.1(i). In terms of '17th-ed installs' I think compliance in that respect could only be achieved by the shed/garage having its own RCBO (since it could not share an RCD with any other circuits). In the case of a TT installation which had an upstream Type S RCD, the shed/garage's RCBO would presumably have to be supplied upstream of that.
The situation you describe, with 32A MCBs in both house and garage/workshop probably would not be non-compliant with 314.1(i), provided that the house MCB served nothing other than the garage feed - since it is incredilby unlikely that the house MCB would operate due to anything other than things happening in the garage (in which case the garage MCB would operate, and create hazards, even if there wasn't one in the house).
Kind Regards, John.