Itmain purpose of the thread was to gain a better understanding of what people interpretations of the rules where, in terms of what could be installed without notification, and one option considered was to add a socket on the end of the existing cooker feed, which would if nothing else, allow the garage to be electrically removed from the house. I never thought this was a good option, but it might have appealed if it had reduced other issues.
Yes, that was my original understanding and, if I understood correctly, at that stage you were thinking of a total 'garage load' of 16A, with the garage being connected to the installation by plugging it in to a 16A socket (fed from the unused cooker circuit) on the outside of the kitchen wall. Is that correct? However,as you say, discussions have moved on from there.
The garage needs some decent lighting, for which I thought a number of 4-5 ft fluorescents was the best option, prehaps 6, and proberbly a 120w pir controled halogen floodlight at the front. It will then need a number of 13amp sockets around the edge to run powertools, drills, anglegriders, chargers, portable lighting (fluorescent handlight and or flood lgiht), etc and given most of these come with 2-4m leads at best my plan as per other workshops ive used would be to have plenty of double sockets, to remove the need for extensions everywhere. And then the single largest power draw, is the welder. I dont really plan to heat the garage as being a large uninsulated steel clad steel framed afair it dont really see it feasable, although if im doing prolonged fine work and it becomes and issue I might invest in a 2kw halogen heater.
Thanks for clarifying - this is obviously closer to scousespark's interpretation than your original proposal. I presume that you would not envisage using more than one of the power tools at once - in particular, not using any other tool whilst using the welder. Is that correct? The heater (which I don't think you've mentioned before), if you got it, would obvioulsy move the goalposts a fair bit (to the tune of nearly 9A).
The welder is an Esab Caddy 160i Inverter Mig, spec sheet is below, which if you do the sums (say 150*20.1/0.82) can draw around 16amps, although it is supplied with a 13amp uk plug (actaully a moulded schuko with adapter) and appears to weld of this, through extension leads, perfectly satisfatorally which given its intended and used as highly portable welder, is very usful.Tech specs for the welder avilable on Esab's website:
http://products.esab.com/Templates/T041.asp?id=179839
In that case, scousespark is right. Even if 'it works', you really shouldn't be running that off a 13A socket - it should be on a 16A socket supplied by its own dedicated radial circuit.
Given it appears the cooker feed is 6mm^2 by current preposal would be to extend this to the garage in 6mm^2 SWA, fed from a 40amp mcb in the houses '17th ed' twin RCD protected consumer unit. Then in the garage fit a consumer unit with a pair of 16amp mcbs each powering a radial of 13amp sockets down each side of the garage, and a 6amp mcb for the lighting, which I understand should give some diversity from the 40amp mcb.
As above, the welder really needs its own 16A socket on a dedicated 16A MCB - and then you could have one or two 16A MCBS supplying radials for the sockets circuits and a 6A one for the lighting. You will certainly get some chance of discrimination between 16A and 40A MCBs, but certainly not guaranteed.
Alternativly it would be possable to have the lighting as a 6amp fcu off one of the radials.
Once you've got a CU in the gararage, you might as well give it its own 6A MCB (unless you run out of 'slots' in the CU).
You could also take the supply from a 40amp switchfuse installed along side the house consumer unit, or shunt the first RCD in the house cu over and put the garages MCB between it and the main switch so it would atleast not be RCD protected till the garage consumer unit.
As previously discussed, if you were to have a garage CU, that would be the best place to have an RCD (with no RCD protection at the house end), to avoid faults in the garage taking out circuits in the house. Using a 40A switch-fuse rather than an MCB in the house would give you a greater chance of discrimination (against 16A MCBs in garage CU), but that would, I think,be about the only advantage (and clearly would be notifiable). If you were going down that (clearly more expensive) route, it would probably make sense to go the whole hog, with, say, a 60A switchfuse and 10mm² cable all the way to the garage, thereby achieving very good discrimination from the 16A MCBs in garage.
Going back to your original reason for posting ('notifiability'), crazy though it might be, it's difficult to argue with BAS's interpreting the Building Regs as excluding
all electrical work in a non-flammable outbuilding <30m² floor area from the need to notify, and many would probably agree with him that having a JB in the kitchen (to extend the cooker circuit to somewhere else) is also not notifiable. If one accepts all that, and if you meet the floor area requirements, then extending the existing cooker circuit to the garage, and everything you do within tyhe gragare (including installing CUs etc.) would presumably be non-notifiable - even if I (and many others) probably find that 'very surprising'.