One would hope not but, again, it does not alter the fact that BS7671 requires a 'suitability for Zone 1' statement in the MIs.
Actually BS7671 does not require such a statement.
The wording in BS7671, namely:
"In zone 1, only the following fixed and permanently connected current-using equipment shall be installed, provided
it is suitable for installation in zone 1 according to the manufacturer’s instructions:"
does not mean such a statement is required; merely that according to the MIs the product is suitable for zone 1.
Stating it is IPX4 means it is suitable for installation in zone 1.