They don't say it's suitable for any particular zone. They don't say it isn't suitable for any particular zone. They only say "suitable for bathrooms".
Quite - so, strictly speaking, installing it in Zone 1 would not be compliant with BS7671, since that would require the MIs to explicitly say that it is "suitable for Zone 1". Don't shoot me - I'm just the messenger
AFAICT, as long as the circuit is RCD protected and the fan is rated IPX4 or better, then all is good. A spark I know told me this earlier:
Well, that may be his/her view, and probably even a sensible view - but, as above, it's not actually what BS7671 says.
"Check that the manufacturers' instructions don't state that it isn't suitable for use in Z1."
As above, that does not help to satisfy BS7671, which says that a fan may be installed in Zone 1
provided it is suitable for installation in zone 1 according to the manufacturer’s instructions. Not saying that it is not suitable is not the same as saying that it IS suitable
. The instructions presumably don't say that it is not suitable for Zone 0, either, but I would hope that you would not regard it as acceptable in Zone 0 (even if it were RCD protected and IPX4), would you?
If it were me, and my house, I would be very happy to take the view you suggest, but if the fan were in Zone 1 and the MIs did not explicitly say that it was suitable for that Zone then I would not claim or pretend that it was compliant with BS7671 (and so could not really criticise anyone who gave it a C2 in an EICR) - but I would lose absolutely no sleep over that