Indeed it is. With a single 2.5mm² cable, the maximum permissible MCB rating would be 20A.the breaker is rated at 32. Is that not a little too high?
Kind Regards, John.
Or 25A?
Indeed it is. With a single 2.5mm² cable, the maximum permissible MCB rating would be 20A.the breaker is rated at 32. Is that not a little too high?
Kind Regards, John.
That's why John wroteOther than the 32Amp on 2.5mm, that is!
If every inch of the cable is Method C, then technically yes (if one could find a 25A MCB for his CU). However, for those obsessed with the deemed-to-satisfy bits of the regs, Appendix 15 talks of only 20A 2.5mm² radial finals, not 25A ones (and FWIW I've personally never seen, heard or come across a 25A radial final).Or 25A?Indeed it is. With a single 2.5mm² cable, the maximum permissible MCB rating would be 20A.
I was not suggesting that 25A MCBs don't exist, merely that it might be difficult (or, indeed, impossible) to find one recommended for the OP's CU. For example, TLC don't offer 25A MCBs for MK, Wylex, Hager, Crabtree or Contactum CUs.http://www.google.co.uk/search?sourceid=navclient&hl=en-GB&ie=UTF-8&rlz=1T4GGHP_en__426GB426&q=b25+mcb
I'm not suggesting they are, but if they don't list a 25A MCB for any of the makes of CUs they sell, I regard that as an indication that, at the least, they are not very 'readily available'.TLC are not the only supplier...
I've personally never seen, heard or come across a 25A radial final
I take it that, despite the absence of words, you agree that few, if any, of the major manufacturers of CUs commonly used in UK offer a 25A MCB for their current ranges of domestic CUs?http://www.google.co.uk/search?sourceid=navclient&hl=en-GB&ie=UTF-8&rlz=1T4GGHP_en__426GB426&q=b25+mcb
No need to apologise - the pouncing was just about par for the course!Sorry, John. I posted the bit about a 25A breaker tongue-in-cheek, but see you've been pounced upon.
That qualifies as 'rare' in my mind!I understand you're not denying the existence of 25A breakers. And you're not denying the existence of 25A radials, just that you have never seen one. I have seen one in this country in 25 years of looking!
Maybe, but would that be 25 Irish amps, or 25 of ours?Doubtless if I went to Ireland, I may see more.
That would make senseProbably the Irish ones. Perhaps they're less efficient as maybe they've had a Guiness & Jamesons chaser.
It is a rating not offered by many.I take it that, despite the absence of words, you agree that few, if any, of the major manufacturers of CUs commonly used in UK offer a 25A MCB for their current ranges of domestic CUs?
That's why John wroteOther than the 32Amp on 2.5mm, that is!
"Provided the MCB is downrated to 20A (or the cable uprated to 4mm² - which I doubt the OP needs), I see nothing wrong with his present set-up." and not just "I see nothing wrong with his present set-up."