Indeed, we might have derailed a bit but hopefully it'll help to convince the OP that this is a job for an electrician.Sure - but, as you imply, it's the Ze that is the saving grace.
Indeed, we might have derailed a bit but hopefully it'll help to convince the OP that this is a job for an electrician.Sure - but, as you imply, it's the Ze that is the saving grace.
Maybe, but he might want to take note of the fact that I am not, never have been and never will be, an electrician!Indeed, we might have derailed a bit but hopefully it'll help to convince the OP that this is a job for an electrician.
You need to know how to apply that knowledge as well though, and I guarantee if you've not run in and made off a 16mm 3 core SWA before you will make a **** of it. Circuit design is important but that includes physically fitting it as well.Maybe, but he might want to take note of the fact that I am not, never have been and never will be, an electrician!
It's what one knows that counts/matters, not whatever label one may (or may not) have attached to oneself
All very true. However, although you suggested that our rather tangential discussion may have "helped to convince the OP that this is a job for an electrician", the discussion had actually been entirely about 'design', rather than the practical skills needed to actually execute the work!You need to know how to apply that knowledge as well though, and I guarantee if you've not run in and made off a 16mm 3 core SWA before you will make a **** of it. Circuit design is important but that includes physically fitting it as well.
I dont disagree with you John, i am just quoting the three basic considerations we must cover by one means or another and these are the initial considerations we are taught 1 or 2 or all 3 of them might be covered by the same OPD or indeed by seperate devices or also by the nature of the load. Then we go on to other considerations like volt drop etc.Indeed - provided, of course, the OPD has an adequate rating for the anticipated loads.
I think your (2) is probably redundant. Since no cable has a neutral with a CSA less than that of the CPC, if the circuit's 'maximum Zs' is satisfied [i.e. your (3) ], then (2) would also inevitably be satisfied.
Kind Regards, John
Fair enough. The one thing I forgot to say was that my comment (obviously) related to TN installations - i.e. when primary fault protection was provided by an OPD.I dont disagree with you John, i am just quoting the three basic considerations we must cover by one means or another and these are the initial considerations we are taught 1 or 2 or all 3 of them might be covered by the same OPD or indeed by seperate devices or also by the nature of the load. Then we go on to other considerations like volt drop etc.
That's obviously the (historical and current) conventional approach (in TN installations) but I do wonder whether it remains a sensible way of thinking today,given that RCDs are dramatically 'better' at detecting (and clearing) L-E faults than are OPDs - and LE fault resulting in a fault current of, say, 100 mA might be enough to kill, yet if ADS was provided by, say, a B32 MCB, the fault current might have to be as high as 160,000 mA before the fault was cleared.My own preference is to have a TN system if possibe and the OPD taking care of earth faults with supplementary protection via RCD usually but sometimes you might have to have an alternative method.
I certainly never knock the concept of redundancy of protective devices/measures (of any sort) but it's interesting to note that we often see people being 'criticised' for putting RCDs in series, but virtually never see people suggesting that one should put them in series! What seems (to me) to be rather illogical is that it is nevertheless far from unknown to see people (like you above, and sometimes me!) advocating redundancy of RCDs, but never advocating redundancy of MCBs - despite the fact that RCDs are easily testable whereas MCBs are (in practice) essentially untestable (and quite possibly as prone to 'stiction' as are RCDs)!!If it needs sole reliance on an RCD working then I prefer two in series and preferably in different environments and preferably of different makes in order to reduce chances of the ill effects of "stiction" although that might mean cascading with a RCD that cant be relied upon for personal protection (certainly not if the fault occours whilst touching, although if tge fault occurs prior to touching then, depending upon the nature of said fault, it might in some cases, disconnect prior touching it)
Overload protection certainly is. However, if an L-E fault creates a fire risk, it is because of excess current flow (through the L as well as anything else), so overload protection ('alone') is again surely enough to give the 'protection against fire', just as it would if the excessive current were flowing through N as well as L - after all, an OPD does not know where an excessive L current has 'gone'.Overload and fault protection is primarily there to protect against fire.
Again, fire risk results from excessive current flow (through L as well as anything else), so (assuming the fault is in a final circuit) will be addressed by OPDs, in the same way that overload currents are addressed. The only additional protection (against fire) that an up-front 100mA RCD would seem to provide is in relation to L-E faults between that RCD and the devices in the CU - but that is an incredibly improbably occurrence (and with TN installations, there is no protection against such incredibly rare events other than from the cutout fuse).Same goes for 100mA RCDs on TT systems,
One can argue about 'what it is there for', but I would say that it does potentially provide considerably more protection against electric shocks than does OPD-based ADS.it's not there primarily to protect against electric shock ...
If you're talking about a TT installation with some final circuits which are not otherwise RCD-protected, then I agree.and is not there for redundancy, it's ensuring ADS in a L-E fault on the supply cable/circuits without RCD protection.
As I said, I would personally never knock redundancy of (any) safety measures. I've observed that we often see people being discouraged from having RCDs ('unnecessarily') in series, and rarely, if ever, see people being encouraged to do it - so, for betteror worse, that is consistent with what you say.I'm sure 30mA RCDs get fitted in series all the time but I'm also sure the wiring regs don't condone that.
A MCB or fuse is overload and fault protection, other than in a TT scenario where the Zs is too high to ensure disconnection. RCDs in TN systems are classed as additional protection.Overload protection certainly is. However, if an L-E fault creates a fire risk, it is because of excess current flow (through the L as well as anything else), so overload protection ('alone') is again surely enough to give the 'protection against fire', just as it would if the excessive current were flowing through N as well as L - after all, an OPD does not know where an excessive L current has 'gone'.
And the price. I don't think it's dangerous, just unnecessary and annoying.As far as I can see, the only significant downside of RCDs in series is a little (probably 'once in a blue moon') 'inconvenience', which I would personally regard as a reasonable price to pay, particularly given that we are led to believe that 'failure' (or, at least, off-spec performance) is not all that rare in in-service RCDs.
Indeed.A MCB or fuse is overload and fault protection, other than in a TT scenario where the Zs is too high to ensure disconnection.
Yes, I realise that's what BS7671 'classes' them as, but that does not alter what I said - namely that they potentially offer much more protection against electric shock than an MCB or fuse ever could.RCDs in TN systems are classed as additional protection.
That's probably generally true, although not true of my TT installation. All of my final circuits have, for many years been RCD- or RCBO-protected but I nevertheless still need up-front 100 mA RCDs in order to provide fault protection to the lengthy distribution circuits.A new TT installation today would likely not need a 100ma RCD up front with the inclusion of 30ma protection for lighting circuits in the 18th
In a field which is moving towards SPDs and AFDDs etc. (the need for which in domestic installations is, to my humble mind, very questionable), I think that the cost of additional RCDs is probably pretty trivial.And the price. ...
I don't think that anyone has suggested that having multiple RCDs is 'dangerous'. I don't think there is any conceivable way in which it could be electrically dangerous. Potential 'danger' would only exist if the device(s) were feeding safety-critical loads (e.g. 'life supporting equipment') but that danger would exist even with just one RCD, but would be increased by their being two or more.... I don't think it's dangerous,....
As I've implied, I'm not sure that it is ever sensible to say that redundancy of any protective devices/measures is 'unnecessary', in that it will always increase safety, particularly when one is talking about devices/systems which are known to sometimes fail in service without anyone being aware that it has happened. If one feels that having a backup for a device which could fail in service is 'unnecessary' one has to ask how 'necewssary' the first one was.just unnecessary and annoying.
Absolutely, but that's not what the fuse is there for. The basic protection against electric shock is enclosures and insulation preventing contact with live conductors. A "fault condition" is basically considered to be a dead short (to N or E or exposed conductive part) and a fuse or MCB protects against that as well as an RCD - and I'd argue less likely to fail due to the simple mechanical designs.Indeed.
Yes, I realise that's what BS7671 'classes' them as, but that does not alter what I said - namely that they potentially offer much more protection against electric shock than an MCB or fuse ever could.
There's no need for inverted commas, in the real world live to earth faults tend to occur when live comes into contact with earth.As I said, I actually do wonder how often OPD-based ADS actually 'works' in the face of real-world (rather than hypothetical 'negligible impedance') L-E faults, whereas an RCD will clear faults due to L-E faults of considerably greater (than 'negligible) impedance (but still potentially dangerous).
Agreed, its good to have a discussion though - a lot of what's in the regs is open to interpretation and there's usually more than one way to skin a cat. The initial question asked was if a cable would be suitable, but it's rarely that simple.I find as an electrician we tend to jump to conclusions without considering all factors. Specially when we are not on site.
You appear to be rather contradicting yourself, given that you previously wrote ...Absolutely, but that's not what the fuse is there for.
.. and, in the absence of RCD protection, it is indeed true that the MCB or fuse is the only thing providing any fault protection. As you go on to say, as far as far as BS7671 is concerned, in TN installations RCDs 'only' provide 'additional protection'. To be 'additional', it obviously has to be additional to something else (i.e. the OPD-based ADS).A MCB or fuse is overload and fault protection .....
Very true, but it's not Basic Protection which we are talking about.,The basic protection against electric shock is enclosures and insulation preventing contact with live conductors.
Indeed it is ("a fault of negligible impedance")A "fault condition" is basically considered to be a dead short (to N or E or exposed conductive part) ....
It does - but (as below) only if it really is a "fault of negligible impedance"and a fuse or MCB protects against that as well as an RCD ...
You may be right about that - I don't know. However, given that one of the main reasons for malfunction of RCDs is said to be 'stiction', and since I would guess that RCDs tend to operate more often than MCBs (most of the many MCBs in my house have not operated in the past 30+ years), I might expect it to be at least a great problem with MCBs.- and I'd argue less likely to fail due to the simple mechanical designs.
Yes, but coming into contact with" and "having a negligible impedance path to" are, in the real world, not the same thing. You surely must have looked at a (correctly 'zeroed') resistance meter whilst 'touching together' two conductors. One often has to fiddle about quite a lot to get the reading anywhere near zero.There's no need for inverted commas, in the real world live to earth faults tend to occur when live comes into contact with earth.