So I’m not going mad then. I thought I had a point!If it's a TN-C-S supply, the 'DNO earth' is actually the neutral feed. If that is broken or 'switched off', then there will be no 'earth' for the installation.
Kind Regards, John
So I’m not going mad then. I thought I had a point!If it's a TN-C-S supply, the 'DNO earth' is actually the neutral feed. If that is broken or 'switched off', then there will be no 'earth' for the installation.
Kind Regards, John
Well, the point you made was seemingly correct, but I'm not sure that it is particularly relevant.So I’m not going mad then. I thought I had a point!
Agreed. However without a reference the generator ‘earth’ will be just floating, potentially resulting in a voltage existing between the generator (which I would think has a metal frame) and the ground.Well, the point you made was seemingly correct, but I'm not sure that it is particularly relevant.
The only reason why one needs earth ('an earth') is because the neutral of the DNO's supply is connected to earth at the transformer. If one has a floating genny supply, that issue does not arise, and the only reason (that I can think of) that some people might consider 'having an earth' to be important would be to facilitate operation of any RCDs (which often won't exist with a temporary genny supply, anyway).
Kind Regards, John
True, but provided the generator output truly is floating, that, in itself, does not present any hazard, any more than does the output of, say, a 'shaver socket',Agreed. However without a reference the generator ‘earth’ will be just floating, potentially resulting in a voltage existing between the generator (which I would think has a metal frame) and the ground.
That may be true of big and/or fixed generators, but I'm sure you will find that many a portable/'standby' generator used 'in the filed' has no earth referencing.Every generator I have ever worked on, okay typically bigger (50-500kva) has an earth stake, so although the generator supplies an ‘earth’ in the form of TNS, it is referenced to true earth
I don't think anyone said it can't be done but making it work and doing it right are different things. BS7430 is inactive now, this from a couple of years ago is a good commentary on different generator setups (and applicable to the UK). There is no one size fits all solution, it depends on the generator and other factors.
Apparently with the help of a computer far far less powerful than what most of us us now have in our pockets, around our wrist or whereverHow did we put man on the moon....
Very true ("needs must"!!) - and I say that as the man who, once upon a time wrote, a rudimentary 'word processor' (and similar with other things like 'spreadsheets'), in Z80 machine code, with the constraint that it had to fit in 8 kB of available storage!" When I look at the size of modern applications, I have to wonder what on earth is in it and how 'sloppy' the programmers are being!But in those days the effort and skill to write tight, highly efficient, single-purpose code was immense. And expensive. And is no longer needed or valued.
And before those days ( of the first computers ) the the effort and skill to design and build hardware was immenseBut in those days the effort and skill to write tight, highly efficient, single-purpose code was immense.