I've had a look through various documents (ENA ER 59/2, The Distrubution Code and internal documents) this morning to see if the answers are there!
I can find no reccomendation for the value of the customer's earth.
That it can be connected to the DNO earth is correct, all the earthing should be solid for this type of installation.
The changeover switch must also operate on the neutral (SP&N or TP&N)
It is clear from all the documents I found in some that the DNO must be consulted and approve the changeover and earthing arrangements, which is chargeable work.
From one of them
I can find no reccomendation for the value of the customer's earth.
That it can be connected to the DNO earth is correct, all the earthing should be solid for this type of installation.
The changeover switch must also operate on the neutral (SP&N or TP&N)
It is clear from all the documents I found in some that the DNO must be consulted and approve the changeover and earthing arrangements, which is chargeable work.
From one of them
Neutral Earthing
The winding configuration and method of earthing connection shall be agreed with the DNO.
In addition, where the Generator‟s Connection Point is at Low Voltage the following shall apply
(a) Where an earthing terminal is provided by the DNO it may be used by a Generator for earthing the Generating Plant, provided the DNO earth connection is of adequate capacity. If the Generating Plant is intended to operate independently of the DNO‟s supply, the Generating Plant must include an earthing system which does not rely upon the DNO‟s earthing terminal. Where use of the DNO‟s earthing terminal is retained, it must be connected to the Generating Plant earthing system by means of a conductor at least equivalent in size to that required to connect the DNO‟s earthing terminal to the installation.
(b) Where the Generating Plant may be operated as a switched alternative only to the DNO‟s System, the Generator shall provide an independent earth electrode.
(c) Where it is intended to operate in parallel with the DNO‟s Low Voltage System with the star point connected to the neutral and/or earthing system, precautions will need to be taken to limit the effects of circulating harmonic currents. It is permissible to insert an impedance in the supply neutral of the Generating Plant for this purpose, for those periods when it is paralleled with the DNO‟s System. However, if the Generating Plant is operating in isolation from the DNO’s Distribution System it will be necessary to have the Generating Plant directly earthed.
(d) Where the Generating Plant is designed to operate independently from the DNO’s Distribution System the switchgear that is used to separate the two Systems shall break all four poles (3 phases and neutral). This prevents any phase or neutral current, produced by the Generating Plant, from flowing into the DNO’s Distribution System when it operates as a switched alternative only supply