GN3 and GN8 cover it I think. It's not that hard.
I still don't really understand. Clashing of the resistance areas of what electrodes with which? Furthermore, in the final analysis isn't it loop resistance (which can't possibly be less than Re) that one is really most interested in?Where the electrode resistance areas can clash, loop testing is only for use where you are testing an electrode on a TT system which has RCD protection. An electrode used as the means of earthing of a system needs to be done the old fashioned way....In other words, under what circumstances could a measurement obtained by loop testing be significantly 'wrong'?
It sounds as if many of you "haven't lived"! Before I had a loop tester, I had to measure electrode resistances with a transformer, ammeter, voltmeter and a couple of earth rodsThe method is completely alien to a majority of sparks bar the likes of Westies men and lightning conductor men who will probably do this a lot. I would have to consult my books on this type of testing as I have never needed to do it before.
The area around the rod can overlap with other electrodes or extraneous conductive parts which too have a resistance area which can give an artificially low reading. As the rod Rob is sinking in, when in use, is nothing to do with the fault path back to the distribution transformer then you need to ask what meaning measuring the rod as part of a TT system is worth. I'll use capital letters to signify Rob's new rod, a loop measurement will give you a reading for tT. It is going to be used as a Tn-s for the house etc and a Tt for the milking area.I still don't really understand. Clashing of the resistance areas of what electrodes with which? Furthermore, in the final analysis isn't it loop resistance (which can't possibly be less than Re) that one is really most interested in?Where the electrode resistance areas can clash, loop testing is only for use where you are testing an electrode on a TT system which has RCD protection. An electrode used as the means of earthing of a system needs to be done the old fashioned way....In other words, under what circumstances could a measurement obtained by loop testing be significantly 'wrong'?
I obviously don't know exactly what Rob did, and it's possible that he did simply measure the EFLI of the installation (with extraneous-conductive-parts connected), in which case what you say above would be correct. However, if one wants to estimate the Re of an earth electrode by loop testing, one tests the electrode in isolation - i.e. although one uses the supply L to undertake the test, one disconnects the rod from the installation and connects it only to the meter. Most loop testers measure both L-E loop impedance and L-N loop impedance. They display the former (usually calling it Zs), but also subtract half of the L-N loopimpedance from it and display the result as 'Re'.The area around the rod can overlap with other electrodes or extraneous conductive parts which too have a resistance area which can give an artificially low reading.
That may be the 'party line' but, as I've explained, electrically-speaking one can (if the DNO's supply is TN) get a very good measurement (and crucially, a measurement which can't be higher than the truth) in the manner I described. In fact, in electrical terms, the only real difference between using a loop tester and a 'proper earth resistance tester' is that, in the latter case, one is 'in control' of the reference electrodes one uses, whereas in the former case one is using the DNO TN earth for that purpose.Rob is dealing with the means of earthing for his own TN system (and a TT system as an aside), the DNOs earthing system has nothing to do with it hence must be left out of any testing.
Not if you use the high current two-lead test, which you would.although one uses the supply L to undertake the test, one disconnects the rod from the installation and connects it only to the meter. Most loop testers measure both L-E loop impedance and L-N loop impedance. They display the former (usually calling it Zs), but also subtract half of the L-N loopimpedance from it and display the result as 'Re'.
OK, if that's how your meter works - but whether the meter subtracts the line impedance automatically or one subtracts it manually, what I wrote about the method still applies. In practice, of course, the line impedance is likely to be almost negligible compared with the resistance of an 'average' earth electrode, but it becomes more significant when dealing with very low earth resistances such as RF is looking for. 'Ignoring' (not subtracting) the line impedance obviously would simply make the measurement more 'conservative' (higher than the truth).Not if you use the high current two-lead test, which you would. This will not display the Re measurement but the line value (separately determined) can be deducted from the total.
Agreed (although, of course, some loop testers/MFTs, particularly older ones, only offer that method) - I wasn't thinking totally straight when I talked about the automatic determination/display of Re. However, as you've said, one can determine it separately and subtract it manually.All true but my main point in answering your previous post is that - you would not use the low-current 'no-trip' method to test/measure a rod.