I have recently installed a new 16 way consumer unit containing 6 x 6a, 5 x 32a and 1 x 40a RCBO's. 6 x light circuits, 5 x socket rings and a cooker outlet (for 5.7kw oven and 4kw hob). I feel competent and I've followed as much spec and calcs as I could find. i have not attempted to cut corners to save time and/or money. this is my home and i wanted to do it properly. I've tested all the circuits, one by one and all on together with no problems - everything worked first time and as it should. I have several questions, so PLEASE be patient...
1) I have split my lounge light circuits in two - thus 2 x 6a RCBO's feed one room. I done this because one of the RCBO's feed a total of 12 x 50w dimmerble halagen spots and the other RCBO 8 x spots (same). I've now been told by an electrician, I should have used 2.5mm and not 1.5mm - is that correct?
2) At the rear of the consumer unit, I have colour coded each cable, or pairs of cables, by taping them together using various coloured insulating tape. For example, I have "grouped", using tape, about 18" of the tails entering the CU. I done this to easily identify each group when connecting them up to the RCBO's and to help those that work on the CU in the future. Again, the electricain has told me that this can cause a fire. true?
3) I have used 10mm cable from the 40a RCBO in the CU to the cooker outlet (about 9m). This will feed a 5.7kw oven and from that, 6mm cable feeding hobs totaling 5kw (dominos). I done this because I thought a 40a RCBO could feed around 13000w. Once agian, the electrician has told be that I've messed up! I should have used 10mm on everything including the feed to the hobs. he also said that a 40a was not enough! True or false?
4) One of the 32a RCBO's at the CU, feeds outside 2 x 2 gang sockets which are RCD protected. He (the electrician) has told me that you should "NEVER" put an RCD on a circuit protected by RCBO's.
5) I installed, from scratch, 3 light circuits and 4 x socket rings (extension, loft conversion and terrace). In doing so, I had to provide a neutral feed to all light switches because I installed X10 light switches. I installed all the switches (20 of them!!!) and they all operated perfectly when commanded to either by switching them on manually or via the computer/mobile phone. the electrician has told me that i could face prosecution for installing neutral feeds to switches!!!!
There are other things he said, but they'll keep for another post. he has told me that the whole lot needs "ripping" out" and doing by a "qualified sparks who knows what hes doing mate". I am so down now. I've spent months and months of research and man hours, not to mention money! I was, and still am, proud of the level of workmanship I have achieved, but now worried that it all may have to be done again. HELP!!
1) I have split my lounge light circuits in two - thus 2 x 6a RCBO's feed one room. I done this because one of the RCBO's feed a total of 12 x 50w dimmerble halagen spots and the other RCBO 8 x spots (same). I've now been told by an electrician, I should have used 2.5mm and not 1.5mm - is that correct?
2) At the rear of the consumer unit, I have colour coded each cable, or pairs of cables, by taping them together using various coloured insulating tape. For example, I have "grouped", using tape, about 18" of the tails entering the CU. I done this to easily identify each group when connecting them up to the RCBO's and to help those that work on the CU in the future. Again, the electricain has told me that this can cause a fire. true?
3) I have used 10mm cable from the 40a RCBO in the CU to the cooker outlet (about 9m). This will feed a 5.7kw oven and from that, 6mm cable feeding hobs totaling 5kw (dominos). I done this because I thought a 40a RCBO could feed around 13000w. Once agian, the electrician has told be that I've messed up! I should have used 10mm on everything including the feed to the hobs. he also said that a 40a was not enough! True or false?
4) One of the 32a RCBO's at the CU, feeds outside 2 x 2 gang sockets which are RCD protected. He (the electrician) has told me that you should "NEVER" put an RCD on a circuit protected by RCBO's.
5) I installed, from scratch, 3 light circuits and 4 x socket rings (extension, loft conversion and terrace). In doing so, I had to provide a neutral feed to all light switches because I installed X10 light switches. I installed all the switches (20 of them!!!) and they all operated perfectly when commanded to either by switching them on manually or via the computer/mobile phone. the electrician has told me that i could face prosecution for installing neutral feeds to switches!!!!
There are other things he said, but they'll keep for another post. he has told me that the whole lot needs "ripping" out" and doing by a "qualified sparks who knows what hes doing mate". I am so down now. I've spent months and months of research and man hours, not to mention money! I was, and still am, proud of the level of workmanship I have achieved, but now worried that it all may have to be done again. HELP!!