2.5mm on a 6A RCBO? No, 1.5mm is more than adequate unless (off the top of my head) completely surrounded by insulation, even then it might be ok.1) I have split my lounge light circuits in two - thus 2 x 6a RCBO's feed one room. I done this because one of the RCBO's feed a total of 12 x 50w dimmerble halagen spots and the other RCBO 8 x spots (same). I've now been told by an electrician, I should have used 2.5mm and not 1.5mm - is that correct?
Can you post a picture?2) At the rear of the consumer unit, I have colour coded each cable, or pairs of cables, by taping them together using various coloured insulating tape. For example, I have "grouped", using tape, about 18" of the tails entering the CU. I done this to easily identify each group when connecting them up to the RCBO's and to help those that work on the CU in the future. Again, the electrician has told me that this can cause a fire. true?
How big is your house? (it is a relevant question) What do the MI's say about electrical connection of the appliances? What kind of hobs are they (ceramic, induction etc) and how many rings? How did you calculate 13kw? 40A may not be adequate for this load. WRT cable size, there is some debate about the sizing of the final connection to cooking appliances but it seems to be generally accepted that if there is no guidance in the MI's then the appliance can be connected with a cable which exceeds the max draw of the appliance but not necessarily as large as the circuit cable. In any case 6mm t&e at 9m length can safely carry 40A, although there may be ambient temperature factor to consider.3) I have used 10mm cable from the 40a RCBO in the CU to the cooker outlet (about 9m). This will feed a 5.7kw oven and from that, 6mm cable feeding hobs totaling 5kw (dominos). I done this because I thought a 40a RCBO could feed around 13000w. Once agian, the electrician has told be that I've messed up! I should have used 10mm on everything including the feed to the hobs. he also said that a 40a was not enough! True or false?
If anything it makes the installation a tiny bit safer because if one RCD was faulty there would be a back-up but it is generally seen at the least as unnecessary and pointless, there are discrimination problems and it can increases the inconvenience in the event of a fault/faulty RCD. Ideal solution would be having a protected/surface run/deeply buried cable on the non-rcd side and have the RCD at the outdoor socket and but simply changing the outdoor sockets for normal weatherproof ones would regularise the setup and satisfy any departures for the regs relating to discrimination and inconvenience. I'm sure there a few threads on here where it has been discussed.4) One of the 32a RCBO's at the CU, feeds outside 2 x 2 gang sockets which are RCD protected. He (the electrician) has told me that you should "NEVER" put an RCD on a circuit protected by RCBO's.
There are problems if you have data cables alongside mains or sharing the same enclosures. There is absolutely nothing wrong with having neutrals at switch location and for an electrician to tell you otherwise suggests he must be a con merchant or dangerously incompetent.5) I installed, from scratch, 3 light circuits and 4 x socket rings (extension, loft conversion and terrace). In doing so, I had to provide a neutral feed to all light switches because I installed X10 light switches. I installed all the switches (20 of them!!!) and they all operated perfectly when commanded to either by switching them on manually or via the computer/mobile phone. the electrician has told me that i could face prosecution for installing neutral feeds to switches!!!!
If you had done much research on here you would have found many people who are told to involve an electrician from the start, or notify building control and find out their procedure for DIY rewire attempts. You have not done this . . . WHY!?There are other things he said, but they'll keep for another post. he has told me that the whole lot needs "ripping" out" and doing by a "qualified sparks who knows what hes doing mate". I am so down now. I've spent months and months of research and man hours, not to mention money! I was, and still am, proud of the level of workmanship I have achieved, but now worried that it all may have to be done again. HELP!!
What were the other things he said?
Lets have some pictures of your work so we can assess your workmanship.