What are the insulation resistance readings from the 'live' conductors to earth?
Before |am told off for doing something illegal, I am a qualified electrician (albeit 25 years ago). I've installed a new stacked (12 x 2) MK consumer unit in my house. A part p qualified friend of my will test the system and certify.
I've completely b*****ed the wiring of a CU and I'm conspiring with someone to lie and break the law.
I take a pride in my workmanship.
Incoming neutral to main switch. Outgoing neutral from main switch to neutral bar 1.
You should have a neutral from neutral bar 1 going directly to RCD1. The outgoing neutral from RCD1 should then supply neutral bar 2. All final circuits fed from RCD1 should have their neutrals connected to neutral bar 2.
You should also have another neutral from neutral bar 1 going directly to RCD2. The outgoing neutral from RCD2 should then supply neutral bar 3. All final circuits fed from RCD2 should have their neutrals connected to neutral bar 3.
You're correct in connecting the neutrals from the RCBOs to neutral bar 1.
...I shall now leave it to my electrician...
Yeah you're probably right. It's not like anyone will carry on regardless if they are not given any advice.