Thanks for the great feedback. I'm starting to favour the tubular heater now, probably either 40 watt or 80 watt. I think 40 watt should be sufficient so I'll buy one to test.

The junction box in the loft is on a 5 amp lighting circuit that runs a total of about 350 watts including lights and an extractor fan. I think it includes an earth but need to check. Is there any reason why I couldn't run a 40/80 watt heater off the lighting circuit on a fused spur? It feels wrong to put it on the lighting circuit, but presumably it would be okay to run a 100 watt lightbulb off that circuit. I don't see much difference! Running it off a ring main would be more invasive.

Fused spurs are not used or needed on a lighting circuit. It is already fused at 5 amp. If you must run it off the lighting circuit all that is needed is a switch.
 
Sponsored Links
Because the designer of the heater probably intended it to be protected by a 13A fuse?
Why? Has he made something so flaky that it has to rely on circuit protection for its own health? The circuit device is there to protect the cable, not for any other reason.
 
There's nothing 'flaky' about taking the expected characteristics of circuit protective devices into account when designing a product.
 
Kind of high for a U.K. immersion heater isn't it? The majority I've ever seen are 3kW elements on 15 or occasionally 20A circuits.
Unnecessarily high for the 3kW immersion, yes. Perhaps the installer thought it might in the future be useful for an electric shower, or he had some 6mm and a 32A mcb to use up
 
Sponsored Links
There's nothing 'flaky' about taking the expected characteristics of circuit protective devices into account when designing a product.
There is nothing but flakiness.

The circuit device is there to protect the cable, not for any other reason.
 
Apart from any generic requirements for obeying/taking-note-of MIs, what rights do electrical equipment manufacturers have to override wiring regulations requirements for overload and fault protections of circuit cables?

If you agreed with me we would both be right. If you don't then I am right and you are wrong. If the HokiKoki2000 Transmogrifier needs its innards to be protected by a 5A fuse then the makers must embed such a fuse in the innards, not insist that it be applied to the circuit supplying it.
 
Apart from any generic requirements for obeying/taking-note-of MIs, what rights do electrical equipment manufacturers have to override wiring regulations requirements for overload and fault protections of circuit cables?
None at all. They aren't.
 
So what would prompt an ultra-vires instruction in an MI other than the knowledge that they'd designed a product which had to rely on a level of circuit protection which they had no right to expect?
 
what rights do electrical equipment manufacturers have to override wiring regulations requirements for overload and fault protections of circuit cables?
None. But they have every right to design their products in such a way that they require a certain level of overcurrent protection for that product and to specify in their installation instructions that such protection should be included.
 
I disagree.

As a basic principle they may not rely on something which is not there to protect their equipment.
 
He is not required to equip it with terminals that can accept the conductor sizes that would be used on such a circuit.

But in terms of protections, yes - the OPD is not there for him, it is there for the circuit cables.
 
Kind of high for a U.K. immersion heater isn't it? The majority I've ever seen are 3kW elements on 15 or occasionally 20A circuits.
Unnecessarily high for the 3kW immersion, yes. Perhaps the installer thought it might in the future be useful for an electric shower, or he had some 6mm and a 32A mcb to use up
Sounds plausible, just somewhat unusual.

30A circuits for electric water heaters are pretty common here, by the way, but the most usual element size is around 4.5kW.
 
If the HokiKoki2000 Transmogrifier needs its innards to be protected by a 5A fuse then the makers must embed such a fuse in the innards, not insist that it be applied to the circuit supplying it.
So if the HokiKoki2000 Transmogrifier requires free access to air to operate properly and safely, does that mean it must come with its own internal air supply and the manufacturer shouldn't be able to specify in his instructions that it be installed somewhere with adequate ventilation?
 