I take it that you can show how and where an air supply is within the scope of electrical installation wiring?
It isn't, but that's the point.I take it that you can show how and where an air supply is within the scope of electrical installation wiring?
You were doing alright there, until you added "cables".the OPD is not there for him, it is there for the circuit cables.
Because the fuse or circuit breaker is not there to protect the innards of his product. If he wants one to do that then he must put it in his equipment.If you accept that the manufacturer may specify in his installation instructions that the HokiKoki2000 Transmogrifier must be located where it will have an adequate supply of air, (or that it must be mounted level, or that it must not be installed where subject to freezing temperatures, or whatever) then why shouldn't he be able to specify that it must be connected to a source of power protected by a fuse or circuit breaker not exceeding X amps?
Says who?Because the fuse or circuit breaker is not there to protect the innards of his product.
What do you mean?You were doing alright there, until you added "cables".the OPD is not there for him, it is there for the circuit cables.
JPEL/64Says who?
That you should have stopped when you got as far as "it is there for the circuit."What do you mean?You were doing alright there, until you added "cables".the OPD is not there for him, it is there for the circuit cables.
I must have missed the news that equipment manufacturers are now bound by the decisions of that particular committee then, if you think that's a valid argument.JPEL/64Says who?
They're not. They're stating their requirements for the proper and safe installation and operation of their equipment. Besides, doesn't BS7671 itself say something about following manufacturer's instructions anyway? So how can it be an attempt to "superimpose" a requirement on BS7671 which BS7671 itself says should be followed?they may not attempt to superimpose their requirements on it.
Yes they are.They're not.
They are stating that for their equipment to be safe to use the normal relationship of Ib ≤ In ≤ Iz may not be used, and that somehow their equipment, which is not within the scope of BS 7671, must be allowed to influence the design.They're stating their requirements for the proper and safe installation and operation of their equipment.
BS 7671 does not say that attempts to subvert the design of the installation because the manufacturer has been unable to make a product which is intrinsically safe should be allowed.Besides, doesn't BS7671 itself say something about following manufacturer's instructions anyway? So how can it be an attempt to "superimpose" a requirement on BS7671 which BS7671 itself says should be followed?
Indeed they do.How do you think you can design the electrical installation of a house without the choice of appliances infuencing it in some way?
The loads which are to be run are bound to have some influence on the wiring put in place to power them.