There will be a drop in temperature along the pipe due to heat lost from the pipes, but a 14 degree drop is excessive.All bar the 4 radiators achieve this at the same temperatures as the flow and return at the boiler. I can get an 18 degree differential on these 4 radiators but the incoming flow temp is only 65 to begin with.
This is really strange. If there is a 14 degree drop when the other rads are on, why no drop when they are off?It's worth noting that these 4 radiators are the last 4 on the system and furthest away from the boiler and pump and when closing all other radiators down the flow temperature achieves 79 degrees at these radiators
Why is the flow set to 80 degrees? At this level the return will never get below 55C, so the boiler will never condense and run efficiently. In this mild weather with outside temperatures around 10 degrees the flow temperature should be below 65C. Try setting the boiler temperature to 70C and balance for a 15-18C difference.
Do you have kW output details of your rads? If not, use the information in the Stelrad Catalogue, page 44. Post the total rad output.