This is a sign of too much air entering the burner.....as per Oilheads post earlier on.
Effectively, its blowing the flame out, especially when the boiler is cold.
John
Without a flue gas analyser, all is guesswork....does he have such a thing?
Just a point - if a new oil pump has been fitted, they are often set very high at the factory, maybe 150 psi, which is usually much too high. This could be the reason for the air door being well open at 15. If I remember, 9 or 10 is usually about right but that's a guess!
John
That makes sense to me. But i don't understand how plumber did not figure it out. lolIf your burner is overfiring, the flame is too far ahead of the nozzle.....maybe that's what's confusing the photocell?
John
If the burner improved when covering up the air intake, then this suggests over aired combustion with flame detachment. The photocell would be obstructed by the diffuser in this case, as confirmed by the retention of flame when the photocell was lit by a torch.
The fact that it does not work with the burner box on is probably a totally different problem. Sort out the burner first, then address the flue problems.
How many 'engineers' have you had to this? You seem to be particularly unlucky, or are you making do with a cheapskate?
Did he leave details of the oil pressure setting ?