New to me house, noted where CU was before buying and got a EIC showing a rewire so all seemed fine, so went to turn off power to move a socket only to find with main isolator off, RCD off and all MCB's off everything still powered up.
So can see Henley block with two outputs so started to look for second consumer unit, in the end noted a small oblong of plaster board missing to left of CU and shining a touch through the hole find there is a old fuse box above the ceiling.
It would seem a false ceiling was fitted when garage made into a flat approx 2005, and the original fuse box was just left where it was. I would suspect it was hard up to original ceiling. House around 1985 build.
Clearly it needs moving, however how and where to is another question. The living room is above the CU so just moving up is not really an option, moving down means house consumer unit will need one to go outside down some steps and into flat to reset anything.
Further forward we have a bathroom then further forward still a utility room, which would be sensible place. However only way I can see of getting feed to utility room is use SWA cable outside the house, then comes the problem of re-connecting circuits to new consumer unit.
Home buyers report says "Ground floors are part solid and part board and joist. The balcony deck is concrete." which means not sure if I can assess cables into fuse board as may be in the concrete balcony deck.
I studied the EIC before buying and thought it seemed a little odd, but did not consider it referred to just the flat, so open for ideas.
Will get carpenter to look at a few jobs required including either temp or other access to fuse box, I would guess old Wilex may be just able to swap fuses for MCB's, but could not assess any cables into it as it is. So think will need hole cutting in ceiling.
So can see Henley block with two outputs so started to look for second consumer unit, in the end noted a small oblong of plaster board missing to left of CU and shining a touch through the hole find there is a old fuse box above the ceiling.
It would seem a false ceiling was fitted when garage made into a flat approx 2005, and the original fuse box was just left where it was. I would suspect it was hard up to original ceiling. House around 1985 build.
Clearly it needs moving, however how and where to is another question. The living room is above the CU so just moving up is not really an option, moving down means house consumer unit will need one to go outside down some steps and into flat to reset anything.
Further forward we have a bathroom then further forward still a utility room, which would be sensible place. However only way I can see of getting feed to utility room is use SWA cable outside the house, then comes the problem of re-connecting circuits to new consumer unit.
Home buyers report says "Ground floors are part solid and part board and joist. The balcony deck is concrete." which means not sure if I can assess cables into fuse board as may be in the concrete balcony deck.
It is now clear not redundant, because built on side of hill there are two ground floors the lower one is the flat (ex garage), upper one the house. And I did not test before exchange, my thoughts were I can test after we moved in.RICS Home Buyers report said:Mains electricity supply. Meter and consumer unit located in lower ground floor kitchen
area.
An old fuse wired consumer unit lies alongside. It is assumed that this is now redundant.
There is reasonable provision of socket outlets. No obvious inadequacies were apparent.
A note on the consumer unit indicates that a test of the installation was due in September
2016. On this basis a test is overdue. It would be prudent to have the installation tested
before exchange.
I studied the EIC before buying and thought it seemed a little odd, but did not consider it referred to just the flat, so open for ideas.
Will get carpenter to look at a few jobs required including either temp or other access to fuse box, I would guess old Wilex may be just able to swap fuses for MCB's, but could not assess any cables into it as it is. So think will need hole cutting in ceiling.