Hi guys,
Just want some advice really.
I had a car charger installed on monday (attempted install)
as the installer was about to wire it up he seemed confused and started saying he couldn't find an earth to my house. after doing some tests on the plug sockets in the house he did some tests and found the resistance was around 2.7k ohms. he stated that it had to be below 200 to fit the unit and told me to ring the DNO, then packed up and left without connecting the unit.
I'll take a picture but after looking around i found what I think has been used as the earth. a piece of flex wired directly into the consumer board and clamped onto a piece of copper pipe that has been buried into the concrete subfloor
I rang the DNO and they said the electrician should have taken a reading from the cutout and they couldn't do anything until he does that.
well he had long gone by that time.
my question is do i just get a copper stake bury it outside, run some 16mm earth to an earthing box and then into the consumer unit.
or do i need to do this by the book and get someone in?
Just want some advice really.
I had a car charger installed on monday (attempted install)
as the installer was about to wire it up he seemed confused and started saying he couldn't find an earth to my house. after doing some tests on the plug sockets in the house he did some tests and found the resistance was around 2.7k ohms. he stated that it had to be below 200 to fit the unit and told me to ring the DNO, then packed up and left without connecting the unit.
I'll take a picture but after looking around i found what I think has been used as the earth. a piece of flex wired directly into the consumer board and clamped onto a piece of copper pipe that has been buried into the concrete subfloor
I rang the DNO and they said the electrician should have taken a reading from the cutout and they couldn't do anything until he does that.
well he had long gone by that time.
my question is do i just get a copper stake bury it outside, run some 16mm earth to an earthing box and then into the consumer unit.
or do i need to do this by the book and get someone in?