200 is the limit above which the OSG advise investigation.
100 is the limit set by NICEIC.
If your supply comes from overhead (sometime underground), then it will have no earth connection with it. This is provided by the consumer,usually through an earth rod.
If yours in underground, if there is no connection to the sheath for an earthing terminal, then it is subterranean TT.
In this case, you need overall protection by a 100mA S type RCD plus further 30mA G type RCD protection for socket outlets.
If you have TT and no RCD's, you are AT RISK!!
However, if you have the RCD set-up as described, 200 Ohms is acceptable, as long as it is no more.
Best solution is to ask the DNO to PME your supply to bring the EFLI right down. Costs up to 100 quid.