For a 5s disconnection, the loop impedance required for a B40 is way less than that.
The rough calc was to consider that the EFLI would be unlikely to be anywhere near that value considering the csa of the cable. Without performing any measurements it would likely be many times smaller, so the fault current would be many times higher. I also was skipping over the time/current charts to establish the minimum EFLI to achieve the 5s disconnection time. At this stage i hadn't even looked up what the max permitted EFLI should be (0.88R) , was merely using engineering judgement and putting a smaller cable in didnt feel right. I have a background in safety critical design, so i can be overly pessimistic with margins as a consequence! Maybe i could have done a better job of formulating some of my thoughts and replies....
Indeed - in fact, one fifth of the figure mentioned (before correcting for Cmin!) - and that because he doesn't seem to understand that the current required to produce an assured magnetic trip of B40 is 200A, not 40A.
Yes you require 200A fault current to achieve the disconnection in a time between 0.1 and 5s. And an overcurrent condition would trip somewhere under 60A, albeit slowly (2000s ish). These presumably being worst case figures since trip current is stated elsewhere as 3 to 5x nominal rating. Again I was too quick in replying with too many assumptions...
You still seem unclear on the difference between overloads and faults.
Whilst i do understand the difference between the two, i think i may have been interchanging them between replies, and over thinking a few things. With a low enough ELFI, the 2.5mm cable will be protected against faults. It was the theoretical and improbable over current condition i was getting worried about, needlessly since a single point would have a single fused plug connected to it.
Which indicates that you are neither clueless nor uninformed.
Can anybody here recommend a few decent guides to the regulations, basic theory etc?
I picked up the OSG, 7671 and the testing guidance note from the IET as I am a member and they offer a decent discount. Ive even got a copy of the regs from 1965 that describe the rules from which this house was wired by! I havent read them cover to cover, more using them as reference guide to check things as i go (like this one). Yes any guides would be appreciated, thank you.
Ultimately im keen to:
a) get it right
b) fully understand the justification
c) have 0 issues arise at the point of inspection (still 1st fixing at the moment)