That bypass valve (the gate valve) only wants to be open a fraction, maybe half a turn at most. A proper bypass valve (which can be set to a specific pressure differential) would be far more useful.
'Suggests' doesn't really do it for me, you'd be amazed how powerful the thermal loop effect is when there's a good uphill stretch between boiler and cylinder.
To verify;
Tell Hive you don't want Ch or dhw heat.
Activate frost stat (and disable the other stat).
Go to motorised valves(s), try manual lever (on Honeywell there is little resistance if the valve is already being driven open).
Go to pump, see if it is running (idiot light or noise).
Then go back to frost stat, deactivate it and check valves and pump again.
'Suggests' doesn't really do it for me, you'd be amazed how powerful the thermal loop effect is when there's a good uphill stretch between boiler and cylinder.
To verify;
Tell Hive you don't want Ch or dhw heat.
Activate frost stat (and disable the other stat).
Go to motorised valves(s), try manual lever (on Honeywell there is little resistance if the valve is already being driven open).
Go to pump, see if it is running (idiot light or noise).
Then go back to frost stat, deactivate it and check valves and pump again.