Installing electric shower from scratch

HI! guys I've been following this subject with interest I have a shower which has been working fine for years on a 6mm cable from a 32amp fuse no probs until now, it keeps tripping on the mcb so I changed the wireing to 10ml and replaced the msb (another 32amp} and put in a new 2pole switch for good measure but it still trips?? I've ordered a 40amp mcb which should solve the problem but still have one in another room just the same as this one ie 32amp 6mm cable working fine. so what do you think the problem is????p.s I've checked the earch connections no probs there.
 
Sponsored Links
don't just blindly uprate mcbs...

what rating is the cooker

do you run anything from the socket on the cooker control plate if there is one and if so what rating is it

if the cooker is just above the design power for a 32A it may be that as the mcb has got older it has got more trip prone (ie the springs have weakened)
 
oops sorry misread shower as cooker

well this eliminates the socket issue but there is still the issue of the showers rating

if the current is within spec on a 32A then you should not blindly uprate the breaker
 
I haven't uprated the breaker I simply replaced it for a new one incase the springs had "weakoned".
 
Sponsored Links
Richardp said:
I've ordered a 40amp mcb which should solve the problem

it's this line i was refering too about blindly updating mcbs

if the shower is within rating for a 32A breaker you should not uprate it

if the shower is just over the rating for a 32A breaker you need to uprate it or you are likely to slowly weaken the replacement
 
OK the reason I'm putting in a 40amp breaker is to cover the new 10 mm cable which I've already put in ready to take a new 10amp shower unit which is on order but wot I would like to know is why the old system packed in (ie 6mm cable with 32amp breaker) in the first place?
this was my original question which I did'nt explain well.
 
i can't answer that without knowing the rating of your existing shower

either there is a slight overload

or the breaker just got weak with age
 
OK its a 9.5kw shower but has been working well for several years which suggests that as you suggest the bracker has got tired which is why I,ve changed it for a new one, however even after changeing it it still trips so i wondered if it could be an earth leak or something else thats faulty in the cu that is affecting it.
 
richard, please note my comments in your other seperate topic. It would be better if you could manage to post only once, this helps keep things together.

Perhaps DIYNOT could move these posts to the other "seperate topic" so as to save us getting lost.
 
is the shower on a rcd? if so that should trip long before the mcb on an earth fault

either way a shower of that size shouldn't be on a 32A breaker even a 40 is too small! 40*230=9300W

you need a 45A breaker (or a 50A if you board maker doesn't do 45A ones) and at least 10mm cable (if it's burried in a wall anywhere it should really be 16mm but very few installer actually bother) for a shower like that

manufacturing tolerances and age probablly both have an efect on exaclty what will trip a breaker
 
Richard, are you 100% sure that this is a 9.5KW shower. This should be drawing 39.5A minimum. Therefore the breaker was way undersized and basically the whole thing dosn't add up. NOTE MY COMMENTS IN YOUR OTHER TOPIC :)
 
A 9.5KW shower supplied with 6mmsq cable protected by a 40A MCB is, in practice acceptable provided the run isn't phenomenal. But this is really on the upper end of compliance. 16mmsq T&E for a shower in domestic? I think NOT :!:
 
INSPECTOR

How about you try and sensibly back up your theory with references to accepted texts, theory and regulations, and then maybe you will get taken seriously.

However, if you can't do this, then FWL is right. You should refrain from making wild and dangerous suggestions that you cannot substantiate.

Remember there are people referring to and using this forum who are very much DIY'ers and they take to heart what is said here.

We owe it to them to give them safe, accurate advice.

Do you want the fact that people are taking bad advice from you on your conscience??

I know I wouldn't.
 