wet between Line(live) and Neutral
will not trip an RCD.
wet between Line(live) and Neutral
Are there any sockets under the sink, one of my previous was caused by a leaky wast pipe and badly positioned socket
What you ordered there, is exactly what you already have - that switch on the left is an RCD.
RCD's are caused to trip by an imbalance of current, comparing the current passing through the live, with that through the neutral. Idea is - if they are not exactly equal, then current is leaking via some other route. The other route, could be through your body, so it trips to protect you.
What many electricians do not appreciate, is that simply turning things off (either at the socket, a switch, or at the MCB) may not prevent the RCD from tripping, if the leakage is neutral to earth leakage. Such faults, especially if intermittent can be very difficult to find. Begin by unplugging anything which can be unplugged, then see if it still trips. If there is no trip of the RCD, then you can gradually add things back in.
If still trips with everything unplugged, then you need some expert help from someone who knows what they are doing, with an insulation tester. That person is obviously not the first 'electrician' you discussed it with. Common causes are oven elements failing, immersion heater elements failing and water which has got into an outdoor light.
Thank you for your message. The idea of ordering that was to plug in one appliance at a time into it in the hope that it would be the adapter that trips off and not the whole circuit - and eventually know specifically which appliance is faulty.
Sounds like it wasn't a good idea though. It's just been delivered so I'll send it back tomorrow.
Indeed. In fact, even if they have different trip ratings, there's no guarantee that the lower rated one will trip first and/or be the only one to trip.When have two RCD's in series and of the same trip rating, either one or both can trip.
Just before going to bed I tried to plug the Dyson Hoover back into the plug
Thanks everybody for your help/advice - I've genuinely learnt a lot!
Is it a Dyson or a Hoover? It can't be both as they are different manufacturers.
You (or someone) need to work out why that socket no longer works. It seems a bit of a stretch to me, for it to simply become dead and cure your tripping RCD issue.
Other then when the water results in an RCD tripping, there is no reason why the presence of water should make a socket 'dead'. As has been said, this matter really should be investigated as a matter of some urgency.I was assuming it was dead because water was getting onto it.