Any comments?
Yes.So the the case with 60amp written on it is the cutout!
It was agreed that the original tails would be removed and replaced with longer, continuous cables. There shouldn't have been connector blocks.They will need access for maintenance/testing for sure. They appear to be floating in the air at present? Red Black single insulation?
Is this the only place they could have gone? Is it close to where the DNO cut out is? How far? Where's the Meter with regards to this?
If you count the cables into the photo and the cables out of the photo it looks suspiciously like a "joint" (the cable connection type)Is there a certificate for the consumer unit install / move?
Problems:
Maximum length of tails is usually 3m.
Tails cannot be concealed in the wall unless more than 50mm from the surface.
The black/red wires look to be smaller than the grey ones - should be the same size.
Also have to ask where these came from, as such colours haven't been available for well over a decade.
Connections must remain accessible, and those black connector boxes must be securely fixed to something, not left hanging on the wires.
What is this taped up mess?
View attachment 151522