I need to clarify that I have a great deal of respect for all recent cotributers and your regular comments, I don't necessarily always agree but that's the nature of the electrical beast. In this instance I'm trying to get to the bottom of the differing opinions rather than just accept them.
If I were to use a generator to run a domestic heater in a building with a mains supply, I'd do an in the head, risk assesment to decide what action needed to be taken.
Perfect examples occurred last winter:
A shed containing tropical fish and the warm air heating from the main building failed, however the mains supply to the shed was only 16A and the various heaters, pumps and lights accounted for about 10A and water temp was dropping. The owner plugged in a fan heater and fairly quickly tripped the supply MCB.
My first and immediate fix was a 5.5KVA generator and 2 fan heaters to warm the air quickly.
No I didn't bond the supplies, both heaters were class I albeit plastic bodied and there was plenty of space between the different supplies, in the order of 4m or so.
However also last year the same generator was used to power fridges and freezers during a brown out, the 5 stood side by side in a row and within easy touching distance are ovens and other appliances, all class I and stainless steel in a commercial setting. Straight away I added the earth/bond no question. Even if it had only been one of those appliances, in the situation my decision and that of my boss would have been the same.
If I were putting in the panel heater (on a genset) into a domestic situation, chances are I'd likey not bond, if the genset was not earthed and only for a short period of time.
I don't believe there is any distinction between generators, for size or number of phases, most generators have an earth point with a warning it must be earthed however the bigger versions frequently have links to be able to dictate the earthing arrangements and running them IT is often quite feasible but I know I'd ever be able to install one of those big heaters into any situation where 'sign off' is required without the CPC of the heater being earthed regardless of the supply status. And most certainly not in any licenced public entertainment situation where multiple inspection layers occur.
In the other thread I mentioned a situation with a battery powered public address system where the on site inspection insisted I use a RCD on a contained (ie with no route earth) inverter supplying several class II devices.
I regularly install self contained PA systems for sound stages and they also get inspected and signed off including checking the bond to the stage structure and that is a 24V battery powered system.
There are British Standards for the methods of earthing/bonding generators/battery supplies, I've been going back through some of my documentation but so far not found any references.
If I were to use a generator to run a domestic heater in a building with a mains supply, I'd do an in the head, risk assesment to decide what action needed to be taken.
Perfect examples occurred last winter:
A shed containing tropical fish and the warm air heating from the main building failed, however the mains supply to the shed was only 16A and the various heaters, pumps and lights accounted for about 10A and water temp was dropping. The owner plugged in a fan heater and fairly quickly tripped the supply MCB.
My first and immediate fix was a 5.5KVA generator and 2 fan heaters to warm the air quickly.
No I didn't bond the supplies, both heaters were class I albeit plastic bodied and there was plenty of space between the different supplies, in the order of 4m or so.
However also last year the same generator was used to power fridges and freezers during a brown out, the 5 stood side by side in a row and within easy touching distance are ovens and other appliances, all class I and stainless steel in a commercial setting. Straight away I added the earth/bond no question. Even if it had only been one of those appliances, in the situation my decision and that of my boss would have been the same.
If I were putting in the panel heater (on a genset) into a domestic situation, chances are I'd likey not bond, if the genset was not earthed and only for a short period of time.
I don't believe there is any distinction between generators, for size or number of phases, most generators have an earth point with a warning it must be earthed however the bigger versions frequently have links to be able to dictate the earthing arrangements and running them IT is often quite feasible but I know I'd ever be able to install one of those big heaters into any situation where 'sign off' is required without the CPC of the heater being earthed regardless of the supply status. And most certainly not in any licenced public entertainment situation where multiple inspection layers occur.
In the other thread I mentioned a situation with a battery powered public address system where the on site inspection insisted I use a RCD on a contained (ie with no route earth) inverter supplying several class II devices.
I regularly install self contained PA systems for sound stages and they also get inspected and signed off including checking the bond to the stage structure and that is a 24V battery powered system.
There are British Standards for the methods of earthing/bonding generators/battery supplies, I've been going back through some of my documentation but so far not found any references.