You are correct of course that if there is any pipework earthing the device the ELCB-v would not operate. .... The problem is as you rightly said will the ELCB-v work? Any alternative path and it would not trip and there is no real way to test it to show it will work. ... Speed is the real problem. ... So on thinking about it can't really be used ...
Indeed, as I said, those would be the problems with what you suggested
However I had come across a ELCB-v last year and the internal resistance of the device was so high that the ELI read as open circuit which is how I found the ELCB-v in the first place. The RCD tester would not work the safety feature stopped it being operated. The test button on the RCD worked but they are between line and neutral so it would.
Indeed. The presence of a VO-ELCB coil (IIRC, usually about 500Ω
in the path to earth would put the EFLI of the circuit up into the clouds, but it would have little effect on the operation of the RCD in most situations. If it did prevent an RCD operating, that would be because it’s presence had reduced the fault current to <30mA, in which case one wouldn’t expect/want the RCD to operate.
My first thought was what happens if I disconnect the earth on the suspect appliance and clearly it would not trip the RCD ...
... unless, as we’ve both said, the earth leakage path was via something (e.g. pipework, or a human being!) other than the CPC
but would be extremely dangerous specially since we suspect an earth fault in the first place ...
Quite so. I can think of few things one could do which would be more dangerous when one already suspected an L-E fault!!
... and I was trying to think of a way to supply the appliance under test without tripping the main RCD.
If the appliance is resulting in sufficient leakage to trip the RCD, then there’s really no sensible/safe way of stopping it tripping the RCD. The sort of ideas you are coming up with (VO-ELCB coils or diodes in the CPC path) are essentially attempts to reduce the fault current to a level which won’t result in tripping. I’m not sure that really helps and, in any event, any such methods (at least, any I can think of) would rely on the (not necessarily true) assumption that the leakage current was travelling along the CPC.
However, as I’ve said, one does not really
need to stop the RCD tripping – one merely needs a method of determining whether the appliance in question has caused a trip which actually happened.
Speed is the real problem. I have used my RCD tester many times and in the main around 12 ms to trip. But I have had items trip in 6 ms on the odd time so looking at less than that. But 10 ms is the lowest guaranteed time i.e. one half cycle. And clearly RCD tripping in 6 ms means it is tripping within a half cycle.
Indeed, but an electronic detector such as I have proposed could be designed so as to be able to detect the current imbalance within those timeframes.
So after consideration I have come to the conclusion there is no way to prove an item with timed functions is not faulty when using a common 30 mA protected supply. We can show as faulty but not as not faulty.
If one had a means of detecting electronically the occurrence of a transient current imbalance >30mA, if that showed that no such imbalance had occurred when it was in-circuit (to the suspect appliance) when the RCD tripped, that would more-or-less ‘prove’ (at least, render it very probable) that the appliance under test did
not cause
that trip – although that would obviously not mean that it never caused RCD trips. However, in practice, if a trip occurred which was not due to the appliance you were testing/monitoring, it would be extremely likely that the ‘culprit’ was something else!
My RCD tester does a great job showing it will trip at 30 mA and within 40 ms but when it tests the device does not trip it puts a 15 mA leakage but does not put any harmonics or spikes on the supply and clearly these can also trip a RCD.
Sure, a regular RCD tester cannot reproduce all the situations which might result in a trip.
So assuming a domestic with two RCD's the only real test is to swap which RCD supplies the suspect device and if then the other RCD starts to trip one has found the problem.
Ultimately, that (or simply replacing the RCD temporarily with a new one) might prove necessary, but swapping the RCDs in a CU is not a trivial exercise, and it would be much nicer if one could first largely eliminate (or ‘convict’!) some suspect appliances by use of a simple plug-in device such as I have postulated.
Kind Regards, John