'Leak' detection for RCD trip troubleshooting

the crunch comes with the £93.60 price tag.
But how much more than a standard RCD of reputable make is that?

The difference could pay for itself in faster identification of suspect appliances.

Plus think how electricians could freak out their customers if they had the SMS messages come to them.

Ring ring....

"Hello"

"Hi, this is Eric the electrician - have you just plugged in something new?"

:mrgreen:
 
Sponsored Links
It may or may not be 'high resolution', but I suspect what you actually mean is 'high sensitivity'
Mmm - not sure Resolution: 0.001 mA Accuracy: 1% + 5 Max Permissible current: 60 A rms
That's what they call it.
Yes, but they call that resolution because it is resolution! It could have a 'resolution' of 0.001 mA (i.e. could display a result such as 20.123A - albeit that's a bit daft with an accuracy of only 1%!) but a low sensistivity such as it could not measure (at all, or reliably) below, say 500 mA.

So, you have indeed confirmed that it has high resolution, but it is implicit in the fact that it is a 'leakage' meter that it also must have high sensitivity (i.e. able to measure currents doen to 'low mA values'). A meter which could measure down to low currents (1mA) but could only display to the nearest mA (i.e. had no decimal points in its display) would be 'high sensitivity' but 'low resolution'.

Kind Regards, John
 
Sponsored Links
Although likely the 10 mA trip would trip before the 30 mA trip or at same time this would not always be the case.

The advert fails to say if active or passive the passive would be better as you could check if it tripped even if the main RCD tripped as well.

40 ms is not very long and RCD's often trip in far less time so even the clamp on meters would need to be fast to beat the RCD tripping in recording the over leakage current.

The in line RCD details gives 30 ms as typical tripping time but if it is an active RCD which the 110 v versions are then one could fit in turn to every item in the house and still not find out which item is faulty if the main 30 mA RCD operates faster than the 10 mA.

So thoughts please. If one used an old ELCB-v and broke the earth sending it through the ELCB-v would the ELCB-v trip before the main ELCB-c? And if this would work would it be safe? OK in a workshop but in a workshop you could use a RCD socket supplied before the main RCD to test or a non RCD protected socket and a meter. What we are looking for is a way to test where all sockets are RCD protected without removing the item from the home where the item has some delayed functions which can cause a RCD to open.

I think the ELCB-v would work but I would be rather uneasy about using one.
 
Well, Here is an in-line' one for £14.26 + VAT. You could easily add a plug and trailing socket for a pound or two more. John
How would you use that to help trace the problem john
It wasn't me who suggested this approach, and it certainly isn't foolproof (see below). I would prefer to use a custom-designed 'monitor/indicator' something like I described in the OP.

As eric has said, if one wanted to use a 10mA RCD for this purpose, then it would be essential that it was a passive one - an active one would inevitably trip when the upstream one did (regardless of what had caused that trip), simply because it had lost its power. With a passive 10mA RCD, it would probably trip instead of, or as well as, the upstream RCD if a 'leak' >10mA arose in the appliance plugged into it, but that is not guaranteed - which is why one could not rely on this approach. A 'positive' answer (10mA RCD trips) will usually be decisive in terms of pointing a finger at the appliance concerned, but a 'negative' answer does not guarantee that it is blameless, even if the upstream RCD has operated.

On the other hand, a custom-designed plug-in in-line device which detected, and indicated, whether a leakage current (L-N imbalance) greater than a certain level (or a number of certain levels) had arisen (even if only for a few milliseconds, before the RCD operated) whilst the device was plugged in would be pretty foolproof. If the upstream RCD had operated, such a device would tell one whether or not that trip has been caused by the appliance/whatever being monitored.

Kind Regards, John
 
So thoughts please. If one used an old ELCB-v and broke the earth sending it through the ELCB-v would the ELCB-v trip before the main ELCB-c?
I don't see why that could be any more guaranteed than, say, a passive 10mA RCD - whether is trips before the RCD would surely depond upon the respective characteristics, sensitivities and speeds of operation of the two devices, plus some 'random' factors, wouldn't it? What makes you think it would trip before the RCD?

In any event, one failing of using a VO-ELCB would be that it would only detect leakage currents which were flowing through the CPC to the appliance. If the leak were occuring to, say, earthed pipework (e.g. in a washing machine) then a VO-ELCB in the supply to the appliance would never operate, even if an RCD in the circuit did.
What we are looking for is a way to test where all sockets are RCD protected without removing the item from the home where the item has some delayed functions which can cause a RCD to open.
Indeed, or just 'random leaks' (rather than 'delayed functions'). As I've said, it would take only very minor modifications to the concept of a cheap electronically-actuated RCD to produce the sort of device I postulated. Simply disconnect the SCR (and the latch which triggers it) and tripping solenoid and, instead, connect the output of the sense amplifier to a little bit of voltage-sensing electronics with some sort of non-volatile display or memory. The only real difference is that one will have replaced the electromechanical consequence of a detected leak (which takes a finite time to happen) with electronic sensing which will be almost instantaneous, and therefore will detect (and 'remember') a leak before an RCD operates.

Kind Regards, John
 
You are correct of course that if there is any pipework earthing the device the ELCB-v would not operate.

However I had come across a ELCB-v last year and the internal resistance of the device was so high that the ELI read as open circuit which is how I found the ELCB-v in the first place. The RCD tester would not work the safety feature stopped it being operated. The test button on the RCD worked but they are between line and neutral so it would.

My first thought was what happens if I disconnect the earth on the suspect appliance and clearly it would not trip the RCD but would be extremely dangerous specially since we suspect an earth fault in the first place and I was trying to think of a way to supply the appliance under test without tripping the main RCD.

Then I remembered the ELCB-v and how it caused problems testing.

The problem is as you rightly said will the ELCB-v work? Any alternative path and it would not trip and there is no real way to test it to show it will work.

So on thinking about it can't really be used but the idea of a device in the earth might.

The next thought was the boat supply where we put diodes in the earth to stop electrolysis. Using these we could give our selves a 1.2 volt lee way and maybe this could be used?

Speed is the real problem. I have used my RCD tester many times and in the main around 12 ms to trip. But I have had items trip in 6 ms on the odd time so looking at less than that. But 10 ms is the lowest guaranteed time i.e. one half cycle. And clearly RCD tripping in 6 ms means it is tripping within a half cycle.

So after consideration I have come to the conclusion there is no way to prove an item with timed functions is not faulty when using a common 30 mA protected supply. We can show as faulty but not as not faulty.

But the question arose because of a guy where the appliance engineer said the installation was at fault not the appliance. We had assumed a single RCD protecting all was the problem but not confirmed.

Theory would say rather than testing appliance all we need to do is test the RCD. However I have had a RCD show as A1 with the RCD tester yet when I swapped it the fault went away.

My RCD tester does a great job showing it will trip at 30 mA and within 40 ms but when it tests the device does not trip it puts a 15 mA leakage but does not put any harmonics or spikes on the supply and clearly these can also trip a RCD.

Many times when my RCD has tripped I have gone to reset it only for it to then trip the other one.

So assuming a domestic with two RCD's the only real test is to swap which RCD supplies the suspect device and if then the other RCD starts to trip one has found the problem.

As to something supplied with only one RCD or even two in series, for example a narrow boat user this is clearly a problem. Having installed a washing machine on a narrow boat believe me one would not want to do it if not required. Dropping down 4 foot to boat floor is not easy with that weight so yes one would want a method of testing on site. Having tried using a 3kW inverter with 6kW peak and it failing on us it is clearly a problem finding a non RCD protected supply.

But other than a narrow boat I don't know of any place where we could not swap RCD's to test. So unless you specialise in narrow boats then not really an issue.
 
You are correct of course that if there is any pipework earthing the device the ELCB-v would not operate. .... The problem is as you rightly said will the ELCB-v work? Any alternative path and it would not trip and there is no real way to test it to show it will work. ... Speed is the real problem. ... So on thinking about it can't really be used ...
Indeed, as I said, those would be the problems with what you suggested
However I had come across a ELCB-v last year and the internal resistance of the device was so high that the ELI read as open circuit which is how I found the ELCB-v in the first place. The RCD tester would not work the safety feature stopped it being operated. The test button on the RCD worked but they are between line and neutral so it would.
Indeed. The presence of a VO-ELCB coil (IIRC, usually about 500&#937;) in the path to earth would put the EFLI of the circuit up into the clouds, but it would have little effect on the operation of the RCD in most situations. If it did prevent an RCD operating, that would be because it’s presence had reduced the fault current to <30mA, in which case one wouldn’t expect/want the RCD to operate.
My first thought was what happens if I disconnect the earth on the suspect appliance and clearly it would not trip the RCD ...
... unless, as we’ve both said, the earth leakage path was via something (e.g. pipework, or a human being!) other than the CPC
but would be extremely dangerous specially since we suspect an earth fault in the first place ...
Quite so. I can think of few things one could do which would be more dangerous when one already suspected an L-E fault!!
... and I was trying to think of a way to supply the appliance under test without tripping the main RCD.
If the appliance is resulting in sufficient leakage to trip the RCD, then there’s really no sensible/safe way of stopping it tripping the RCD. The sort of ideas you are coming up with (VO-ELCB coils or diodes in the CPC path) are essentially attempts to reduce the fault current to a level which won’t result in tripping. I’m not sure that really helps and, in any event, any such methods (at least, any I can think of) would rely on the (not necessarily true) assumption that the leakage current was travelling along the CPC.

However, as I’ve said, one does not really need to stop the RCD tripping – one merely needs a method of determining whether the appliance in question has caused a trip which actually happened.
Speed is the real problem. I have used my RCD tester many times and in the main around 12 ms to trip. But I have had items trip in 6 ms on the odd time so looking at less than that. But 10 ms is the lowest guaranteed time i.e. one half cycle. And clearly RCD tripping in 6 ms means it is tripping within a half cycle.
Indeed, but an electronic detector such as I have proposed could be designed so as to be able to detect the current imbalance within those timeframes.
So after consideration I have come to the conclusion there is no way to prove an item with timed functions is not faulty when using a common 30 mA protected supply. We can show as faulty but not as not faulty.
If one had a means of detecting electronically the occurrence of a transient current imbalance >30mA, if that showed that no such imbalance had occurred when it was in-circuit (to the suspect appliance) when the RCD tripped, that would more-or-less ‘prove’ (at least, render it very probable) that the appliance under test did not cause that trip – although that would obviously not mean that it never caused RCD trips. However, in practice, if a trip occurred which was not due to the appliance you were testing/monitoring, it would be extremely likely that the ‘culprit’ was something else!
My RCD tester does a great job showing it will trip at 30 mA and within 40 ms but when it tests the device does not trip it puts a 15 mA leakage but does not put any harmonics or spikes on the supply and clearly these can also trip a RCD.
Sure, a regular RCD tester cannot reproduce all the situations which might result in a trip.
So assuming a domestic with two RCD's the only real test is to swap which RCD supplies the suspect device and if then the other RCD starts to trip one has found the problem.
Ultimately, that (or simply replacing the RCD temporarily with a new one) might prove necessary, but swapping the RCDs in a CU is not a trivial exercise, and it would be much nicer if one could first largely eliminate (or ‘convict’!) some suspect appliances by use of a simple plug-in device such as I have postulated.

Kind Regards, John
 
There are, and one has to wonder what is the difference between the cheapest ones, like the above, and those costing many times more, many of which appear to have a similar spec.

However, without modification, I don't think that (m)any of these clamp meters could be used for the sort of 'monitoring' we're talking about - most have an 'auto off' function which switches them off after a minute or three 'to save the batteries' - and that also begs the question as to how long the batteries would last if it were left switched on continuously for hours or days.

It's possible that the 'auto off' can be disabled on some, but I've never seen such functionality on a meter. On the plus side, even some of the cheapest ones (like the above) have a min/max facility (i.e. a memory). It would, of course, also be necessary to have a 'breakout lead' to clamp it to (presumably L+N, not E), but that's no real problem.

Kind Regards, John
 
ok thanks john, as you say it would need to be a latching rcd and i didnt see any indication that one was.

we once used 6 plug in latching rcds at about £ 30 each and temporary put a circuit on an mcb to help locate a tripping problem once.
 
ok thanks john, as you say it would need to be a latching rcd and i didnt see any indication that one was.
I presume that by 'latching' you mean 'passive', since that is what one would want - i.e. an 'ordinary' (as in CUs etc.) passive RCD - i.e. one that did not 'trip' as a result of lost power, but only in response to detecting an L-N imbalance. As I'm sure you know, RCD sockets and RCD plugs often are 'active' ones (which would be no good for the purpose being discussed) - so I suppose it's possible that the in-line one might also be 'active'.

Kind Regards, John
 
Yes, i get a bit confused with active/ passive, till recently plug in units were labelled as latching and non latching and as you well know many need manual reset as there possibly used for lawnmowers , motor driven machinery
 
Yes, i get a bit confused with active/ passive, till recently plug in units were labelled as latching and non latching and as you well know many need manual reset as there possibly used for lawnmowers , motor driven machinery
Indeed, the terminology is pretty confusing. I used to find it very difficult to remember which was 'passive' and which was 'active (since it's not intuitively obvious - at least, not to me!). Then someone sugegsted that I thought about it in terms of a power cut - in that situation, a 'passive' one remains passive (i.e. 'does nothing', just remains in its 'on' state) - and I've remembered that every since!

Kind Regards, John
 