- No deviations from BS7671
- TT not observed or tested
- Uo = 240v?
- Main switch = 60898 (and not tested as an RCD)
- Service cut out = 60898 & rating incorrect anyway
- MPB in dining room? Not necessarily wrong, just odd
- No maximum demand filled in
- No serial number for test instruments used
- Upstairs sockets on a 32a breaker with 2.5 but not tested as a ring
- Reference method left blank
- Lights down is on a 10a breaker (this may have been changed after the original install, hence different brand)
- Is it me or does it say complies to BS7671:2012?
- Excellent Ze for a TT??
- TT not observed or tested
- Uo = 240v?
- Main switch = 60898 (and not tested as an RCD)
- Service cut out = 60898 & rating incorrect anyway
- MPB in dining room? Not necessarily wrong, just odd
- No maximum demand filled in
- No serial number for test instruments used
- Upstairs sockets on a 32a breaker with 2.5 but not tested as a ring
- Reference method left blank
- Lights down is on a 10a breaker (this may have been changed after the original install, hence different brand)
- Is it me or does it say complies to BS7671:2012?
- Excellent Ze for a TT??