Ah, anything in the garage is just what I have inherited - I haven't touched any of that!
I have not seen one RCD in the picture and it is clearly very old.
I am assuming one of those wires (bottom or right) goes to a switch?
I would guess since wired there have been many changes including how the water and gas get to the property and it is likely it also has some old ELCB-v fitted so one has to be careful bonding as it could make things worse not better.
When I came to do an upgrade once the owner was very good with his question he said I know it all needs doing but can't afford to do it all now so assuming to be done over 5 years what would you recommend I get done each year. So I split the work into 5 doing of course most dangerous bits first.
So talk to your electrician and work out a plan with him.
It was constructed of two small rooms, a shower room and a pump room, each with its own light. While we were doing the roof we took the opportunity to extend it slightly, moving the end walls by just over a metre and inserting a third small room in the middle.
You've got a shower room and a pump room? That's got to be a hell of a power shower.
If I understand your proposal correctly, you're going to need a switch-fuse in the feed to the SWA going to the poolhouse and also possibly one in the feed to the 'boiler room'. The RCD for the filler pump could be in the poolhouse. However, I'm sure the electrician will understand all these requirements.I suppose the question is whether (in effect) 2 cores of the 10mm2 SWA can be connected directly to the Henley or it must go through another switch/isolator (which the electrician seems to have left out)??
If I understand your proposal correctly, you're going to need a switch-fuse in the feed to the SWA going to the poolhouse and also possibly one in the feed to the 'boiler room'.
The RCD for the filler pump could be in the poolhouse.
However, I'm sure the electrician will understand all these requirements
same thing - a combination of a (simple,manual) switch and a fuse.A switch-fuse or a fused switch, or are they the same thing?If I understand your proposal correctly, you're going to need a switch-fuse in the feed to the SWA going to the poolhouse and also possibly one in the feed to the 'boiler room'.
Unless I'm misunderstanding the nature of the box labelled "63A RCD for filter pump only" (see below), there is no over-current protection on whatever is going into the boiler room other than the supplier's service fuse.There is no feed in the boiler room, just a loop on the filter pump circuit for the timer.
An RCD, per se, offers no protection against over-current (only against leakages to earth) and, in any event, it is downstream of the SWA. If the connection between the supply and a CU is more than 2-3 metres in length, a fuse (other than the supplier's service fuse) upstream of that connection is required.What does that do then? If it feeds to a 100A RCD in the CU at the other end, or does it just protect the other end of the cable?
As above, I may be misunderstand what's going on - in particular what is happening in that box labelled "RCD" - does it perhaps contain MCBs? Whatever, as I've said, whatever is going on in the boiler room needs to be protected by an upstream fuse (or MCB).I think it needs to be in the garage, as it has to connect to the timer, otherwise he then needs to run another cable all the way back to the boiler house to go through the timer (the timer is connected to a pump on the central heating system which pushes the hot water through the heat exchanger for the swimming pool).The RCD for the filler pump could be in the poolhouse.
Unless I'm misunderstanding the nature of the box labelled "63A RCD for filter pump only" (see below), there is no over-current protection on whatever is going into the boiler room other than the supplier's service fuse.
An RCD, per se, offers no protection against over-current (only against leakages to earth) and, in any event, it is downstream of the SWA. If the connection between the supply and a CU is more than 2-3 metres in length, a fuse (other than the supplier's service fuse) upstream of that connection is required.
As above, I may be misunderstand what's going on - in particular what is happening in that box labelled "RCD" - does it perhaps contain MCBs? Whatever, as I've said, whatever is going on in the boiler room needs to be protected by an upstream fuse (or MCB).
Not necessarily, in view of what you now tell us about that box labelled "63A RCD", namely ...Ah, yes, I see that now. So a switchfuse would be expected to go between the mains feed and the 63A RCD (the small CU in the garage) as over-current protection?Unless I'm misunderstanding the nature of the box labelled "63A RCD for filter pump only" (see below), there is no over-current protection on whatever is going into the boiler room other than the supplier's service fuse.
Given that it's a mini-CU with MCBs, if it's close enough to the supply (which it probably will be), you wouldn't need the switch-fuse I've been talking about, BUT ........ This is a self contained circuit which runs:
Mains > 2 way CU (63A RCD, 16A and 32A MCB) > loop on 32A MCB to boiler house for timer > 25m of SWA to poolhouse > switch > filter pump.
The timer has to be there, as it is connected to the heating pump.
I'm confused as to where this SWA is coming from. In your diagram, it appears out of the mini-CU in the garage. From what you've said above, it sounds as if it doesn't go through any MCB in that mini-CU. If that's the case, then that one would need a switch-fuse.Yes, if he says we can do what I am proposing, then the supply would run 25 metres before the poolhouse CU (in which case it presumably needs to be 25mm SWA to carry that sort of load all the way, and a switchfuse once it gets there, prior to going in to the CU?) This is a different circuit which goes:
Mains > (not sure yet... was thinking to connect it directly to 2 cores of the SWA, but the existing is 10mm and I think it needs to be 25mm to carry the full mains safely(?) > CU in pumproom (100A RCD leading to 6A (lights), 40A (sauna), 16A (sockets - might do away with the sockets), 40A (shower)
Yes, if he says we can do what I am proposing, then the supply would run 25 metres before the poolhouse CU (in which case it presumably needs to be 25mm SWA to carry that sort of load all the way, and a switchfuse once it gets there, prior to going in to the CU?) This is a different circuit which goes:
Mains > (not sure yet... was thinking to connect it directly to 2 cores of the SWA, but the existing is 10mm and I think it needs to be 25mm to carry the full mains safely(?) > CU in pumproom (100A RCD leading to 6A (lights), 40A (sauna), 16A (sockets - might do away with the sockets), 40A (shower)
I'm confused as to where this SWA is coming from. In your diagram, it appears out of the mini-CU in the garage. From what you've said above, it sounds as if it doesn't go through any MCB in that mini-CU. If that's the case, then that one would need a switch-fuse.
Given that it's a mini-CU with MCBs, if it's close enough to the supply (which it probably will be), you wouldn't need the switch-fuse I've been talking about...
OK, I think I may now understand. The two cores going to the pumproom are simply 'passing through' that mini-CU, from the supply to the CU in the pumproom - is that correct? If so (a) those cores would need switch-fuse protection and (b) given the size of SWA you are thinking aout, there's no way that you are going to be able to do that wiring within a standard 'mini-CU, if that's what we are talking about - at the least, you would need a decent sized one. However, in view of the need for a swith-fuse, an alternative arrangement would probably be used - e.g. terminating the SWA in another box and taking feeds to that from (a) the mini-CU and (b) from the Henleys, via switch-fuse (for the supply to the poolroom CU).The way I was drawing it, the 4 core SWA is attached to the small CU in the garage. 2 of the cores take the outlet from this CU to the filter pump. The other two cores just take power directly to the other CU in the pumproom.I'm confused as to where this SWA is coming from. In your diagram, it appears out of the mini-CU in the garage. From what you've said above, it sounds as if it doesn't go through any MCB in that mini-CU. If that's the case, then that one would need a switch-fuse.
So, 2 cores go through the mini CU (and MCB within that) in the garage. The other two cores go to the pumproom where they go through the other CU (and MCBs within that).
Two different circuits, making use of the 4 cores as two pairs.
If, as in the normal domestic installation, the distance from the supply (meter) is less than 2-3 metres, then additional protection of that cabling is not deemed necessary. However, if the distance from supply to CU is longer than that, fuse protection is considered necessary.I'm curious now why proximity to the supply would mean it wasn't necessary...?Given that it's a mini-CU with MCBs, if it's close enough to the supply (which it probably will be), you wouldn't need the switch-fuse I've been talking about...