Ok, so what can I do to make the radiators release more of the heat going into them, thereby giving me more heat and reducing the return temp?
As I say, I'm only getting a 5C difference from in to out. This is whilst the boiler is burning away. When it takes a break, which it periodically does, them the in and out temperatures at radiators seem to equalise a bit. As mentioned before, all the rooms have TRVs apart from the one where the thermostat is and that radiator always seems to be the hottest.
How about the flow rate from the boiler? Could that be too high so that the water is being pushed through the radiators too quickly?
Would closing the lockshield a bit not help to keep more heat in the radiator?
As explained already, a rad releases a certain amount of energy based on its mean temperature and the room temperature, in the example you gave you said you had flow/returns of 49/43C with a room temperature of 20C, this is a mean temperature of 46C, you simply cant get that rad to release any more heat and maintain 20C without changing that mean rad temperature and thats it in black and white, we only showed that by increasing the flow temperature to 64C and reducing the flowrate (automatically via the TRV which senses the room temperature) to give a return temp of 28C that the room temperature will still be maintained at 20C because the mean rad temperature is exactly the same at 46C = (64+28)/2. but you get a higher condensing effect = higher boiler efficiency = lower gas consumption.Ok, so what can I do to make the radiators release more of the heat going into them, thereby giving me more heat and reducing the return?
The in/out temperatures will neary equalise depending on how long the boiler is off.As I say, I'm only getting a 5C difference from in to out. This is whilst the boiler is burning away. When it takes a break, which it periodically does, them the in and out temperatures at radiators seem to equalise a bit. As mentioned before, all the rooms have TRVs apart from the one where the thermostat is and that radiator always seems to be the hottest.
Have you checked that the TRV heads (actuators) have been attached properly, ie with the index to max, 5 or whatever the max setting is, before they are installed?.
The faster the flowrate the greater the output due to the smaller flow/return dT and the higher mean temperature. A TRV will just throttle down to give a reduced flowrate and mean rad temperature to maintain the desired room temperature except that the pump head is exceptionally high at say 6M as the TRVs cant overcome a dP of 6M.How about the flow rate from the boiler? Could that be too high so that the water is being pushed through the radiators too quickly
Why do you want to keep more heat in the rad?, closing in the L/shield to throttle the flowrate will reduce the mean rad temperature if this is what you want.Would closing the lockshield a bit not help to keep more heat in the radiator?