Just following your leadwinston1 said:No need to shout.
I thought your philosophy applied to all instructions?If they don't know they should not be doing electrics at all.
Just following your leadwinston1 said:No need to shout.
I thought your philosophy applied to all instructions?If they don't know they should not be doing electrics at all.
OK - put knowing if the instructions are wrong to one side for a minute.If they don't know they should not be doing electrics at all.
You have contradicted yourself. If your first priority is safety then you must have the installation periodically inspected and tested as REQUIRED by the IET Wiring Regulations.I would pay for a proper inspection report, but funds are tight after piling everything into the purchase. First priorty is safety
You have contradicted yourself. If your first priority is safety then you must have the installation periodically inspected and tested as REQUIRED by the IET Wiring Regulations.
It could be a 50A switch.One other concern is that the oven circuit has a 50A mcb, but the cooker isolator will likely only be 45A.
No, it's fine. The oven will never draw 45AMaybe this is also too high for the fixing method(in oval conduit in plaster, above ceiling below upstairs floorboards)? Is either of these discrepancies likely to be a problem at a future inspection? e.g. over rated fuse for the accessories\fixing method?
It could be a 50A switch.
No, it's fine. The oven will never draw 45A
Just installed by someone who likes wasting copper and doesn't understand.
Any domestic cooking appliance will be happy on a 32A MCB with 4mm² cable installed to method C (6mm² in conduit).
Another thing I noticed is that the 10mm cable goes through the backbox(45mm, looks like plenty of space in there) of one the ring main sockets.
It has its insulation on and must have been done as space is tight to run the cables down, but is this normal practice? e.g. 2 cables from different circuits in one back box? I'm guessing not as the 2 way light switching on the stairs does this also, but perhaps the oven circuit is a special case?
It shouldn't be (but who knows with the level of 'inspectors' nowadays?).I just checked, it is a 45A MK socket and isolator
isn't the fuse also there to protect the cable and accessories against short circuit?
Would it be coded on an inspection?
It shouldn't be (but who knows with the level of 'inspectors' nowadays?).
The fuse IS there to protect the circuit but the oven cannot overload it (draw more than it's rated load) so overload protection could be omitted by the regulations as long as fault protection is satisfactory - which, with 10mm² it will be, assuming it is not miles long.
That's a short circuit - so, comes under fault current as opposed to overload.What about a phase to neutral mechanical fault? is that just presumed to be unlikely?
Not really, that determines whether the CPC can handle the prospective earth fault current until disconnection by the MCB.Is the fault protection related to the infamous adiabatic equation?
You need the Loop measurements.I was trying to punch the numbers on that one to check the mini kitchen consumer unit fault tolerance.
(12m 10mmT&E on 40A mcb 80A 30ms RCCB supplying 2 x 4 meters of 2.5mm T&E each on 20A mcbs and a 32A mcb on 10mm for the hob outlet)
You would.It seems with modern fuses(type B) you would be hard pushed to fail on that score with the 4mm cpc in 10mm T&E?