Hi. The short form of this question is whether or not anyone can see anything in the regs which prevents the MPB being bonded to water pipework at more than one point (provided the conductor remains continuous).
More detail .... my (10 mm²) MPB has been religiously connected, per regs, to pipework within 600mm after the water meter. However, this is totally ineffective for the intended purpose, since the bonding is thereby on the supply side of a plastic-bodied flow sensor (about 1000mm from meter). Bonding to the pipes in the property (which is what matters to me) is therefore dependent upon the strapping across the flow sensor, currently much smaller (looks like 4mm²) than the MPB itself. Even if that strapping were upgraded to 10mm, matching the MPB, it would make nonsense of the requirement for an unbroken MPB, and I would prefer to not be dependent for effective bonding on two further screwed terminations.
The most obvious 'sensible' solution would be to simply move the MPB connection to a point about 1200mm from the meter, on my side of the flow sensor. However, if I did that, there would be no guarantee that some 'Jobsworth' inspecting the installation in future would not feel that the absence of a connectuion within 600mm of the meter was non-compliant. I am therfore inclined to leave the present (silly) connection close to the meter, but to also bond the same MPB to pipework on my side of the plastic; there is enough slack in the cable to do this without breaking the conductor. I would certainly sleep more soundly knowing that there was proper direct bonding to the metal pipework in my property, and this has surely got to be within the spirit of the regs.
What do people feel about this, and can you see anything in 544.1.2 (or elsewhere) which precludes bonding tge MPB to pipework in more than one place?
Kind Regards, John
More detail .... my (10 mm²) MPB has been religiously connected, per regs, to pipework within 600mm after the water meter. However, this is totally ineffective for the intended purpose, since the bonding is thereby on the supply side of a plastic-bodied flow sensor (about 1000mm from meter). Bonding to the pipes in the property (which is what matters to me) is therefore dependent upon the strapping across the flow sensor, currently much smaller (looks like 4mm²) than the MPB itself. Even if that strapping were upgraded to 10mm, matching the MPB, it would make nonsense of the requirement for an unbroken MPB, and I would prefer to not be dependent for effective bonding on two further screwed terminations.
The most obvious 'sensible' solution would be to simply move the MPB connection to a point about 1200mm from the meter, on my side of the flow sensor. However, if I did that, there would be no guarantee that some 'Jobsworth' inspecting the installation in future would not feel that the absence of a connectuion within 600mm of the meter was non-compliant. I am therfore inclined to leave the present (silly) connection close to the meter, but to also bond the same MPB to pipework on my side of the plastic; there is enough slack in the cable to do this without breaking the conductor. I would certainly sleep more soundly knowing that there was proper direct bonding to the metal pipework in my property, and this has surely got to be within the spirit of the regs.
What do people feel about this, and can you see anything in 544.1.2 (or elsewhere) which precludes bonding tge MPB to pipework in more than one place?
Kind Regards, John